20 amp gfci to a 15 amp circuit

I'm wanting to replace a regular outlet with a gfci out. I have a 20 amp gfci but the curcuit breaker is a 15amp breaker with 14/2 wire. Can I still use this gfci or do I need to get a 15 amp gfci? Would it be a fire hazard if I used the 20 amp gfci?
 
  #2  
Old 03-26-06, 10:51 AM
bolide's Avatar
Member
Join Date: Jan 2006
Location: PA
Posts: 1,725
Upvotes: 0
Received 1 Upvote on 1 Post
Originally Posted by gorden2440
Can I still use this gfci?
No. Receptacles on a 15A circuit may not be over 15A per NEC 210.21(B).


> do I need to get a 15 amp gfci?
Yes.


> Would it be a fire hazard if I used the 20 amp gfci?
In theory someone could plug in a 20A load.
 
  #3  
Old 03-26-06, 10:54 AM
fixitron's Avatar
Member
Join Date: Dec 2005
Location: Warren, Vermont
Posts: 327
Upvotes: 0
Received 0 Upvotes on 0 Posts
If it is really a 20 amp GFCI (one slot will be the shape of a 'T'), then no. Someone could plug in a device rated for 20 amps (such as a large air conditioner) and overload the circuit.
If it is actually a 15 amp outlet (just the two parallel slots and ground), but is rated for 20 amps "feed-through" (ie.-downstream loads), then you can use it on a 15 amp circuit.
 
  #4  
Old 03-26-06, 11:52 AM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,246
Upvotes: 0
Received 0 Upvotes on 0 Posts
Most GFCI receptacles are 15 amp receptacles, but rated for 20 amp pass through protection.

If the GFCI receptacle you have will accept a 20 amp plug then you need a different receptacle. otherwise you can use the receptacle, assuming you are in the US and there is no local code stipulating otherwise.
 
  #5  
Old 03-26-06, 01:22 PM
G
Member
Thread Starter
Join Date: Mar 2006
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
It must be a 15 amp because it only has the two parallel slots(no t slot) but it says 20amp 125v on the side of it. Why is that?? Thanks for the info.
 
  #6  
Old 03-26-06, 02:16 PM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,246
Upvotes: 0
Received 0 Upvotes on 0 Posts
Most GFCI receptacles are 15 amp receptacles, but rated for 20 amp pass through protection.
 
 

Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: