Adding 20 AMP circuit to office

Reply

  #1  
Old 03-27-06, 08:31 AM
Member
Thread Starter
Join Date: Feb 2006
Posts: 9
Adding 20 AMP circuit to office

I would like to install a new 20 AMP circuit to my office. The one problem with this is I don't really have a good direct route. What I was thinking was to possibly follow an existing ethernet cable run that goes up from the crawlspace through a closet up to my office on the second floor. My question is, is this a good idea?

Thanks,
Wes
 
Sponsored Links
  #2  
Old 03-27-06, 09:11 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
No. Keep low voltage cables (Ethernet, coax, telephone, etc) separated from line voltage cable by at least one foot. Cross them only at right angles.
 
  #3  
Old 03-27-06, 12:16 PM
Member
Thread Starter
Join Date: Feb 2006
Posts: 9
Thanks. I will keep that in mind. What about if I DIDN't have the coax wire in the closet? Do you think it is a good idea to run electrical through a closet?

-Wes
 
  #4  
Old 03-27-06, 03:21 PM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
To run electrical cable through a closet would require protection. Either you would have to use conduit or you would have to block the cable in the corner with wood, for example.
 