High-Hat Thermal Switch Problem
#1
Member
Thread Starter
Join Date: Feb 2005
Location: Media, PA
Posts: 174
Upvotes: 0
Received 0 Upvotes
on
0 Posts
High-Hat Thermal Switch Problem
THIS IS TOTALLY CRAZY..and DRIVING ME CRAZY...EVEN THE NEIGHBORS REMARK !!
and I cannot work in my office at night....one High-Hat fixture simply goes off and on...off and on...and you won't believe this: I replaced the ENTIRE FIXTURE....with a new Halo 6" "can"....and it STILL OCCURS. It's like this house is HAUNTED.
There are 8 other older high-hats working perfectly.
HOW CAN THIS BE ?
I'M READY TO TEAR DOWN THE ENTIRE CEILING....MAYBE THE ENTIRE HOUSE.
This has been going on for 2 years now.
WHY IS ONE, UNO, Fixture not able to work ?
There is nothing special about it's location....drywall ceiling....no insulation around it...
plenty of open space.
and I cannot work in my office at night....one High-Hat fixture simply goes off and on...off and on...and you won't believe this: I replaced the ENTIRE FIXTURE....with a new Halo 6" "can"....and it STILL OCCURS. It's like this house is HAUNTED.
There are 8 other older high-hats working perfectly.
HOW CAN THIS BE ?
I'M READY TO TEAR DOWN THE ENTIRE CEILING....MAYBE THE ENTIRE HOUSE.
This has been going on for 2 years now.
WHY IS ONE, UNO, Fixture not able to work ?
There is nothing special about it's location....drywall ceiling....no insulation around it...
plenty of open space.
#2
> There is nothing special about its location....
Not exactly. Is it the last one on its line?
What size bulb is in it?
Trace the cable back to the previous junction box or can.
That's most likely where the ghost lives.
Tearing down the house is only the third best choice.
Not exactly. Is it the last one on its line?
What size bulb is in it?
Trace the cable back to the previous junction box or can.
That's most likely where the ghost lives.
Tearing down the house is only the third best choice.
Last edited by bolide; 03-16-06 at 12:32 PM.
#3
Member
Thread Starter
Join Date: Feb 2005
Location: Media, PA
Posts: 174
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yep...last one in the line.
Using brand new 65w flood....
must I rewire this....
or reduce the wattage ....
or what ?
Why is the last in line so susceptible ?
Using brand new 65w flood....
must I rewire this....
or reduce the wattage ....
or what ?
Why is the last in line so susceptible ?
#4
> last one in the line.
Excellent.
> must I rewire this....
Not likely, just tighten the loose connection.
> or reduce the wattage ....
Is this by chance a 60W can with a 65W bulb in it?
> Why is the last in line so susceptible?
It's not.
What you need to do is relax, answer the questions to the best of you ability, and follow directions.
If you managed to replace the can, you can easily open the another and inspect the wiring in it.
Either the black or the white wire has a bad connection.
You could figure exactly which one. But it is safer just to check them both.
First you have to figure out which can is next to last.
Do you know which one or do you need assistance?
Excellent.
> must I rewire this....
Not likely, just tighten the loose connection.
> or reduce the wattage ....
Is this by chance a 60W can with a 65W bulb in it?
> Why is the last in line so susceptible?
It's not.
What you need to do is relax, answer the questions to the best of you ability, and follow directions.
If you managed to replace the can, you can easily open the another and inspect the wiring in it.
Either the black or the white wire has a bad connection.
You could figure exactly which one. But it is safer just to check them both.
First you have to figure out which can is next to last.
Do you know which one or do you need assistance?
#5
Bolide: another problem I have seen is the installation of non IC cans and allowing insulation to fall down around it, causing the heat build up and thermo click out. Just a thought.
#6
> another problem I have seen is the installation of non IC cans and allowing insulation to fall down
> around it, causing the heat build up and thermo click out.
He specified no insulation. Might be first floor.
What happens with a 65W miniflood in a 60A can?
> around it, causing the heat build up and thermo click out.
He specified no insulation. Might be first floor.
What happens with a 65W miniflood in a 60A can?
#7
It's not out of the question that both fixtures are defective from the factory ...they could both be from the same batch.
#8
Originally Posted by Andrew
It's not out of the question that both fixtures are defective from the factory ...they could both be from the same batch.
Getting cans from the same batch more than two years apart is not too likely, at least not at a warehouse store.
The poor good does seem to have a lot of negative energy surrounding him. So that would be exactly his luck to get the one in a thousand that is defective from the factory.
The symptoms don't sound much like a defect.
Either he has been using a 65W flood all along in just this one 60W can or there is a problem with the wiring.
There aren't many other possibilities. The latter makes the most sense to me if we are not missing other relevant details - like it's the only 60W can.
#9
Member
My guess is that there is a poor connection at the can just upstream. Some Halo cans use wire nuts and others use a compression fitting similar to a backstab (the trade name escapes me). I suggest opening the JBox at the can feeding the problem one and redoing the connections.
#10
Member
Thread Starter
Join Date: Feb 2005
Location: Media, PA
Posts: 174
Upvotes: 0
Received 0 Upvotes
on
0 Posts
> must I rewire this....
Not likely, just tighten the loose connection.
Not likely, just tighten the loose connection.
I just have 2 wire nuts to make the connection from the conduit that I cut which feeds the can.
> or reduce the wattage ....
Is this by chance a 60W can with a 65W bulb in it?
Is this by chance a 60W can with a 65W bulb in it?
What's really wierd is that this new can has a frequency of going off and on at about the same rate as the old one.
What you need to do is relax, answer the questions to the best of you ability, and follow directions.
If you managed to replace the can, you can easily open the another and inspect the wiring in it.
Either the black or the white wire has a bad connection.
You could figure exactly which one. But it is safer just to check them both.
If you managed to replace the can, you can easily open the another and inspect the wiring in it.
Either the black or the white wire has a bad connection.
You could figure exactly which one. But it is safer just to check them both.
Also, if it were a connection problem, wouldn't the light just stay off completely ?
First you have to figure out which can is next to last.
Do you know which one or do you need assistance?
Do you know which one or do you need assistance?
only my arm.
#11
Member
Hi Mark - With the power off remove the bulb and trim piece. There will be a baffle plate inside with the bulb socket. You can unscrew the baffle plate and lower it down (the wires are attached so be careful). Once it is out of the way, you can reach up and remove the J Box cover (its held in place by a spring latch - no screws to remove) to access the connections. The Halo can is designed to allow access from inside the can. It's a little tight, but you should be able to remake the connections or at least see if one of them has loosened.
I've had the exact problem you describe and the cause was a loose connection in a wire nut. I just tugged on the wires and wire nuts and one of the stranded wires fell out.
I've had the exact problem you describe and the cause was a loose connection in a wire nut. I just tugged on the wires and wire nuts and one of the stranded wires fell out.
#12
Originally Posted by marksimms
Uh....WHICH CONNECTION ?
> What's really wierd is that this new can has a frequency of going off
> and on at about the same rate as the old one.
There is nothing weird about this.
It's the same problem because you haven't done anything about the problem.
There was nothing wrong with the can you replaced.
> Again, which connection ?
In the next-to-last can.
> if it were a connection problem, wouldn't the light just stay off completely?
No.
> what's the trick ? I can't get my head thru the hole, only my arm.
I assume you've seen Wayne's answer by now.
#13
Member
Thread Starter
Join Date: Feb 2005
Location: Media, PA
Posts: 174
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks...but...
I just stuck my hand up there, opened the "door" of the j-connector where the leads were tied-together, and re-tightened them. I then moved around the lead lines coming from the "other" can. After testing this with the can hanging OUT of the ceiling, it appeared to no longer be shutting off and on.
However, when I inserted the can back into the housing in the ceiling, ONCE MORE, the blinking started back up.
This really seems like a thermal switch problem, but how can it be after I replaced the entire can ?
One thing I must mention is that I never replaced the existing housing....I just got a new 6" "can" and it fit inside of the old housing with no problem.
However, when I inserted the can back into the housing in the ceiling, ONCE MORE, the blinking started back up.
This really seems like a thermal switch problem, but how can it be after I replaced the entire can ?
One thing I must mention is that I never replaced the existing housing....I just got a new 6" "can" and it fit inside of the old housing with no problem.
#15
Member
Thread Starter
Join Date: Feb 2005
Location: Media, PA
Posts: 174
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Nope...you were right.
I "overrode" the thermal cut-off switch....and natch, the same blinking occurs.
Thus, the problem is NOT thermal.
The problem is "upstream".....but it's tough to say exactly WHERE.
The room has 4 hi-hats.....I just gotta guess which is the "second-to-last" in line....
and pull that one out. Probably safe to bet it is one of the two closest....
although with "this old house", I've been fooled before.
Thus, the problem is NOT thermal.
The problem is "upstream".....but it's tough to say exactly WHERE.
The room has 4 hi-hats.....I just gotta guess which is the "second-to-last" in line....
and pull that one out. Probably safe to bet it is one of the two closest....
although with "this old house", I've been fooled before.
#16
Member
Thread Starter
Join Date: Feb 2005
Location: Media, PA
Posts: 174
Upvotes: 0
Received 0 Upvotes
on
0 Posts
FIXED ! The nightmare is over...
Finally "went to work"....pulled the entire J-Bar down....took apart all connections....and then "discovered" the old J-Bar "unit" must have had it's > thermal overload protector (which was faulty, natch !). I by-passed that bad boy...put the unit back in place.
All is well now.
Bottomline: experience counts in these hairy problems....I had no idea there would be an overload in the j-unit....but a pro would have known this immediately.
Thanks to all who responded.
All is well now.
Bottomline: experience counts in these hairy problems....I had no idea there would be an overload in the j-unit....but a pro would have known this immediately.
Thanks to all who responded.