Installing undercabinet lighting
#1
Member
Thread Starter
Join Date: Mar 2006
Location: NJ
Posts: 20
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Installing undercabinet lighting
I will be adding undercabinet lighting by direct wiring them to nearby outlets. Is there wiring that I can use besides standard 12 or 14 gauge Romex? Since each light only draws about 40watts, I would prefer to use a much smaller cord that is approved for in-wall use. Am I simply limited by the size of the circuit they are on?
Thanks,
DVAB
Thanks,
DVAB
#2
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,245
Upvotes: 0
Received 0 Upvotes
on
0 Posts
If this is a kitchen and if you are in the US and if you are talking about counter top receptacles then you cannot do this.
You cannot use "cord" at all.
If the lights are designed to hard wired then they need to hardwired with the appropriate size cable for the circuit, that means 12-2 or 14-2, for a 20 amp or 15 amp circuit respectively.
You cannot use "cord" at all.