NM cable straight out of wall

Am I allowed to have NM cable (Romex) come straight out of drywall, through a kitchen cabinet and enter a metal box on the outside of the drywall, provided that no NM cable is exposed in the room?

e.g.

-----------------------------------------------------------
NM Cable (in between studs) | Drywall | Cabinet | Metal box
-----------------------------------------------------------

Thanks,

Antun
 
Sponsored Links
  #2  
Old 04-02-06, 09:05 AM
Member
Join Date: Aug 2005
Location: San Francisco, CA
Posts: 749
Received 0 Votes on 0 Posts
Originally Posted by antun
Am I allowed to have NM cable (Romex) come straight out of drywall, through a kitchen cabinet and enter a metal box on the outside of the drywall, provided that no NM cable is exposed in the room?

e.g.

-----------------------------------------------------------
NM Cable (in between studs) | Drywall | Cabinet | Metal box
-----------------------------------------------------------

Thanks,

Antun
I believe this is ok, if what you're saying is tha you are mounting the box to the inside of the cabinet, rather then to the drywall, which would mean you'd need to cut a hole in the cabinet..?

This is done frequently when installing undercabinet lighting as well. As long as you don't strip the jacket off the romex inside the wall or before it hits the box, I believe you're fine.
 
  #3  
Old 04-02-06, 12:44 PM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
The cable cannot be exposed and subject to damage. Generally speaking, in the back of a cabinet of drawers would be okay. However, an open cabinet would not be okay.

Protect the cable with a piece of conduit, or block it with a piece of wood or something.
 
  #4  
Old 04-02-06, 01:41 PM
Member
Thread Starter
Join Date: Jan 2004
Location: San Francisco
Posts: 103
Received 0 Votes on 0 Posts
Thanks - if I do need to use conduit, can the conduit finish in the drywall, but not be attached to anything (such as a metal box behind the drywall)?

-Antun
 
  #5  
Old 04-02-06, 01:54 PM
bolide's Avatar
Member
Join Date: Jan 2006
Location: PA
Posts: 1,909
Received 0 Votes on 0 Posts
> if I do need to use conduit, can the conduit terminate in the drywall?


Yes, protective conduit does not require a fitting.

You can use just a RNC box connector with no conduit at all.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: