Ground Rod for Sub Panel in Garage

125amp sub panel in detached garage, 50' from house . . .

One or two ground rods?

1/2 inch, or, 5/8 inch?

#4 or # 6 ground wire to ground rod(s)?

Thanks!
 
Sponsored Links
  #2  
Old 04-02-06, 04:48 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
One rod, possibly two. I typically install just one for such an application. Your inspectors may enforce two.

1/2" non-ferrous, or 5/8" steel/iron coated.

#6 is all that is required to a ground rod(s) alone.
 
  #3  
Old 04-02-06, 04:52 PM
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
for subpanel most common to use one ground rod but few area might requried 2 rods but keep in your mind that the netrual and ground wires are kept separted.

#6 is very common and you should have no trouble with this but i will check with your inspector for latest issuse with ground rods it might be little diffrent other wise it pretty uniform on this issuse

Merci , Marc
 