NEC for "old work"

Reply

  #1  
Old 04-04-06, 07:26 AM
Member
Thread Starter
Join Date: Dec 2005
Location: USA
Posts: 3,188
NEC for "old work"

I recently added an outlet and a couple of closet lights. I had to fish the wires within the walls for the outlet and the light switches, Obviously the NM-B cable is just hanging out in the stud bays without stapling. The "old work" plastic boxes don't have clamps or connectors. Does the NEC allow this or is it silent.
 
Sponsored Links
  #2  
Old 04-04-06, 07:50 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,342
NM-B does not have to be stapled when it is fished into a finished wall. Staple it properly anywhere that you have access to the studs.
 
  #3  
Old 04-04-06, 07:51 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
The NEC allows this. The walls are considered the means of securing the cable. The old work box should have a means of securing the cable where it enters, which is often just a piece of plastic.
 