Old 04-05-06, 10:45 AM
So, i'm jogging down one of the streets close by, and I pass one of about 4 lift stations (lucky me). Anyway, we have overhead utility, and all the lift stations, except the newest one use 3 transformers to drive the station. The newest lift station uses 2 transformers, and there is no connection to the 3rd primary wire. So, my question is: Is there a technique of driving the pump motors on only 2 legs?
Old 04-05-06, 10:58 AM
They are using a transformer connection known as open delta to supply the three-phase power. It only requires two transformers but the supply is limited to less than the full transformer rating.
Old 04-05-06, 12:01 PM
Old 04-05-06, 05:00 PM
thanks for those tutorials. I now know a bit about open delta. I remain confused, since my lift station does not tap into the 3rd phase primary at all.
Old 04-05-06, 05:54 PM
The system may have an open wye primary, where the two primary coils are tapped between primary phases and neutral.
-Jon
Old 04-05-06, 09:27 PM
bolide's Avatar
It connect to three wires two hots and neutral.
The neutral connection might not be visible from the sidewalk, but it's possible (and usual) to run three-phase with two ungrounded and one grounded conductor.
In fact, in some places you might see only three wires on the pole.