Service panel indicator lamps

Reply

  #1  
Old 04-26-06, 07:26 PM
JoggingGuy's Avatar
Member
Thread Starter
Join Date: Mar 2006
Location: USA
Posts: 19
Question Service panel indicator lamps

I found a generator interlock kit for my service panel main breaker. But when you are switching the entire utility, there is no indicators of what has power and what doesn't, so I am unable to tell when the power comes back on

Is there a code-compliant way to tap the large wires coming into the box so I can mount an indicator lamp in the panel? TIA
 
Sponsored Links
  #2  
Old 04-26-06, 07:49 PM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
In a word, no. Watch your neighbor's houses.
 
  #3  
Old 04-27-06, 05:32 AM
Member
Join Date: Jan 2004
Location: Oregon
Posts: 1,219
In principal, you _can_ do this. NEC 230.82 lists the equipment which may be placed _before_ the main service disconnect, and suitable metering instruments and instrumentation transformers are permitted items.

However I know of no suitable products for this application. You would need to contact metering companies and find out if any of their products are suitable for use in service equipment.

Additionally, because the main service conductors coming into your panel are unswitched and unfused, I strongly recommend that when you find a suitable product, you have it installed by a professional electrician. This is _not_ an area where you want to learn from your mistakes.

-Jon
 
  #4  
Old 04-27-06, 09:21 AM
bolide's Avatar
Member
Join Date: Jan 2006
Location: PA
Posts: 1,909
In principal, no contact or connection is required whatsoever to detect the presence of AC voltage.
 
  #5  
Old 04-27-06, 01:06 PM
Member
Join Date: Jan 2005
Location: Sterling Heights
Posts: 308
Originally Posted by JoggingGuy
I found a generator interlock kit for my service panel main breaker. But when you are switching the entire utility, there is no indicators of what has power and what doesn't, so I am unable to tell when the power comes back on

Is there a code-compliant way to tap the large wires coming into the box so I can mount an indicator lamp in the panel? TIA
JG,
That's the main reason I didn't use a generator interlock kit on my existing service.....

The interlock kit is a cheaper effective way to go. But with a transfer panel, since main breaker in the main panel in never switched off, any of the remaining circuits in the main panel can be used to energize a night light or something else to alert you when the power is restored.

Also, the transfer panel has watt meters so you can monitor the loads and keep them in a safe range instead of guessing or relying on calculations.

To me, the cost of adding the transfer panel far outweighed the savings of an interlock on the main panel!
Phil
 
  #6  
Old 04-27-06, 02:00 PM
Member
Join Date: Oct 2005
Location: USA
Posts: 1,152
my Greenlee voltage detector will pick up my feeders thru a 2" pcv conduit. It also detects OK when placed within 1/4" of the main breaker. Of course, not as convenient as having a pilot light at the panel.
 
  #7  
Old 04-27-06, 07:13 PM
JoggingGuy's Avatar
Member
Thread Starter
Join Date: Mar 2006
Location: USA
Posts: 19
Thanks for the help guys
 