Question Wiring 2 AC Units

I am up against a wiring project, I have

the following units Mitsubishi Mr. Slim
Product: Indoor unit Model MS12TN

http://www.mrslim.com/Products/itemD...&ProductID=978


Click on download the full specifications:

I need to wire up
2 of the indoor units
2 of the outdoor units


Am I allowed to share
the 2 indoor units on the same circuit?
Am I allowed to share the 2
outdoor units on the same circuit?

What would be the best way to wire this?

Thanks,
I am still a novice
 
Sponsored Links
  #2  
Old 05-03-06, 07:30 PM
Member
Join Date: Nov 2004
Location: CA
Posts: 2,041
The outdoor units cannot be combined. Notice it says maximum fuse ( breaker ) size 15 amps. You must follow this instruction, and of course a single 15 amp breaker is not sufficien for 2 units.

The indoor units, if the specs are correct, only draw 0.6 amps, which seems low, but it is just a fan. So 2 of these could be on a single 15 amp breaker. A dedicated circuit for each would be a "cleaner" set up.
 
  #3  
Old 05-03-06, 11:35 PM
CFS
CFS is offline
Member
Thread Starter
Join Date: May 2006
Posts: 2
Thanks a whole bunch

Thanks For your Help you are such a great resource!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
'