flood light

I currently have a flood light with two lights on it, one to the right and the other to the left and empty in the middle. I want to add another to the middle socket (usually a motion is put there) My question is, is it an overload to throw in another socket, I guess it would be 450 watts for all three lights.
 
Sponsored Links
  #2  
Old 05-06-06, 05:32 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,968
You will be pulling 3.75 amps, so if you have a 15 amp circuit and nothing else is on the circuit, you are ok.
 