Portable Generator Hook Up

Question: Can I hook up my portable generator to my Garage subpanel?

I have a professionally installed 60 Amp sub panel in my garage that feeds diectly from my main house panel.

In the case of a power failure.
1- Could I shut off my main breaker that feeds my main house panel.
2- Switch off all unwanted breakers (I.e. hot water, electronic equipment, wall receptables, baseboard heaters) and leave only my well pump, sewer pump, and fridge/freezer switched on.
3- Plug my portable generator into my subpanel into a 220V plug in to feed what remains on in my main main panel.

When power returns, I do the steps in reverse.

Does this make sense? Any concerns/problems with this setup?

Regards,

Eric
 
Sponsored Links
  #2  
Old 05-19-06, 08:44 AM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
Absolutely positively NOT. Doing so is extremely dangerous and against code.
 
  #3  
Old 05-19-06, 08:52 AM
N
Member
Thread Starter
Join Date: May 2006
Posts: 2
Received 0 Votes on 0 Posts
Thanks for your response Bob.

I am trying to understand the concern. If the main power breaker from the meter to the main panel is OFF, there is no longer a connection to the GRID. The generator becomes the new GRID feed. As long as the generator is turned OFF and unplugged before quicking the main breaker back on, I can't see why it would pose a problem.

Can you elaborate on this?

I appreciate your time and input.

Regards,

Eric
 
  #4  
Old 05-19-06, 08:58 AM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
It poses a problem because the neutral is still connected to the grid, and because there is no way to ensure that the main breaker is turned off.

Someone who doesn't know any better, or you yourself may forget to turn off the main breaker or may think it is turned off and you end up powering the grid.

If you did this and someone was hurt or injured because of this you would be charged. If someone dies, you would likely have plenty of time to think about it in jail.
 
  #5  
Old 05-19-06, 09:41 AM
bolide's Avatar
Member
Join Date: Jan 2006
Location: PA
Posts: 1,909
Received 0 Votes on 0 Posts
time bomb in the garage

Originally Posted by Nutra
As long as the generator is turned OFF and unplugged before quicking the main breaker back on, I can't see why it would pose a problem.
But there is nothing to ensure that this occurs. A proper interlock or transfer panel ensures that this does occur. Humans make mistakes. If you think that you never would, you are mistaken once again.

This is one mistake that is avoidable by using the correct equipment for the job.
 
  #6  
Old 05-19-06, 09:58 AM
F
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
Received 0 Votes on 0 Posts
I will agree with Bodine and Racraft on this matter and you will need a lnterlock kit or transfer switch.

I have seen some crazy hook up with their portable generator how they dealt with this.

it did show up quite few other forums as well as we will give you a fair warning please heed our warning to save your life on this matter.

this is a good graphic example what will happend if you forgot to turn main breaker off while the generator is running what it will do is backfeed to the power company grid and from your geneator run 120/240 volt when it hit the transformer it will boost the voltage to high as 7200 volt or more and it can hit the unexpecting lineworker[s] and hurt them very serious.


The electric transformer DO work both way so that one reason why we say have interlock or transfer switch to prevent it happend

the power company take this matter very serious so please respect the safety for everyone here

Merci, Marc
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: