conduit fill question

Hi All,

Question concerning conduit fill requirements. Iím looking in the NEC in Chapter 9, and I see that under the notes for Table 2 it states that the requirement are not meant for protection of conductors over short runs.

I need to do exactly this: from my subpanel I need to run conductors approximately 6 feet to j-boxes either on the studs or roof eaves. Not sure what table to follow here or what my max is for 12 or 14 awg conductors.

Thanks!
 
Sponsored Links
  #2  
Old 06-06-06, 03:33 PM
nap's Avatar
nap
nap is offline
New Member
Join Date: May 2006
Location: north
Posts: 4,163
Received 0 Votes on 0 Posts
Look at note 4. A nipple 24 inches or less is allowed to be filled to 60% and derating per 310.15(B)(2)(a) does not apply. You are well past the 2 foot rule.


For conduit fill go to Annex C.

Don't forget to derate per 310.15(B)(2)(a)

but if you are using mixed sizes, you get to figure it out manually using , I think , tables 4 and 5 and 5a of chap 9
 
  #3  
Old 06-06-06, 05:26 PM
Member
Thread Starter
Join Date: Aug 2005
Location: San Francisco, CA
Posts: 749
Received 0 Votes on 0 Posts
Originally Posted by nap
Look at note 4. A nipple 24 inches or less is allowed to be filled to 60% and derating per 310.15(B)(2)(a) does not apply. You are well past the 2 foot rule.


For conduit fill go to Annex C.

Don't forget to derate per 310.15(B)(2)(a)

but if you are using mixed sizes, you get to figure it out manually using , I think , tables 4 and 5 and 5a of chap 9
Just checked and I was wrong; I'm right at 24 inches. So according to table C.1, I can fit 61 - 12awg THHN conductors in a 1 1/2" EMT? Am I on the right track? Or because it's less than 24 inches, is there another calc?

Thanks.
 

Last edited by fuente; 06-06-06 at 05:44 PM.
  #4  
Old 06-06-06, 08:02 PM
nap's Avatar
nap
nap is offline
New Member
Join Date: May 2006
Location: north
Posts: 4,163
Received 0 Votes on 0 Posts
Actually that table is for 40% fill. the note I gave allows up to 60% fill so that should be 1 1/2 times as many or 90 #12 thhn. Actually if you calculate it out using tabes 4 and 5 of chap 9 it comes out to 100 wires. And you do not have to derate them.

Now if you have this inspected and you have a picky inspector, if the nipple is 24 1/2 inches, he can ding you on it.


Is that enough wires for you??
 
  #5  
Old 06-06-06, 08:57 PM
Member
Thread Starter
Join Date: Aug 2005
Location: San Francisco, CA
Posts: 749
Received 0 Votes on 0 Posts
Originally Posted by nap
Actually that table is for 40% fill. the note I gave allows up to 60% fill so that should be 1 1/2 times as many or 90 #12 thhn. Actually if you calculate it out using tabes 4 and 5 of chap 9 it comes out to 100 wires. And you do not have to derate them.

Now if you have this inspected and you have a picky inspector, if the nipple is 24 1/2 inches, he can ding you on it.


Is that enough wires for you??
wow that seems like a lot of conductors !! Sounds good, that's plenty for the number of circuits I'm running.

Thanks nap.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: