hot tub wiring
Old 06-11-06, 10:39 AM
B
hot tub wiring
I am wiring my 40 amp hot tub for 240. The tub is approximately 8 feet from my main panel on a cement patio. I have also purchased a 50 amp GFCI spa panel.
Here are my questions:
1) could the spa panel be next to the main panel (which is between 5 and 10 feet from the inner wall of the tub)?
2) based on these distances and amps, I plan on using #6 wire. Is this the best gauge, or could I use #8?
3) the tub will draw 40 amps, but is it okay to have a 50 amp dedicated breaker in the main and a 50 amp spa panel?
Thank you in advance for any help you might be able to provide.
Bryn
Old 06-11-06, 12:38 PM
R
Is the main panel inside? Where would the spa panel be, inside or outside?
Old 06-11-06, 12:59 PM
B
panel is outside
Panel is on the outside of the house. Since the tub is only about 8 feet from the panel, I thought I could put the spa panel on the wall of the house next to the main panel.
Old 06-12-06, 10:13 AM
I
Received 43 Votes on 41 Posts
I would just use a 40A double pole GFCI breaker in the main panel. The subpanel is not required in your case.
I'm not sure on this one specifically. I know you cannot have other receptacles in the 10' zone, but don't know about the panel.
Use (4) #8 THWN conductors in conduit -- black, red, white, green.
No. If the installation instructions say 40A, you need a 40A breaker.
Old 06-12-06, 09:03 PM
B
hot tub wiring
Ben,
Thanks for the great advice. It should be straightforward from here.
Bryn