Is there any code requirement for the height a GFI has to be mounted like "x inches" above a bathroom counter top or sink?

Thanks guys!
 
Sponsored Links
  #2  
Old 06-12-06, 02:37 PM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Code requires a receptacle on a 20 amp circuit within 36 inches of the outside edge of the sink basin. I have not heard of height requirements. Remember that the receptacle itself does not have to be a GFCI receptacle, it must only be GFCI protected.
 

Last edited by racraft; 06-13-06 at 01:30 PM.
  #3  
Old 06-12-06, 02:56 PM
Sparky375
Visiting Guest
Posts: n/a
Bathroom outlets must be within 36" of basin and not lower than 12" if mounted on the side of cab.
 
  #4  
Old 06-12-06, 04:39 PM
Member
Thread Starter
Join Date: Jan 2005
Location: USA
Posts: 585
Thanks guys. You differ on the 26" or 36" but we'll be within 12" so I don't have to question it...

I'll go up 10" above sink height hoping that I don't splash that much.
 
  #5  
Old 06-12-06, 05:32 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
Methinks Bob made a typo. It is 36" with NO minimum height. The only minimum is what Sparky wrote about it being installed actually in the side or face of the base cabinet.

I use 44" to-the-top of the box.
 
  #6  
Old 06-12-06, 10:13 PM
Member
Thread Starter
Join Date: Jan 2005
Location: USA
Posts: 585
OK then I have a similar question for my other bath remodel...

The double sink vanity is supposed to be made with a center row of drawers. The top isn't really a drawer but a hair dryer storage nitch. A GFI is supposed to be in the nitch so the hair dryer can be stored away w/the cord tucked in. It's being made by a cabinet maker and is not some type of production type UL approved product. Is ther any issue w/this GFI mounting position?
 
  #7  
Old 06-13-06, 03:19 AM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
The receptacle itself? No.
As long as it is accessible.

That receptacle will not meet the code required one though.
 
  #8  
Old 06-13-06, 04:53 AM
Member
Thread Starter
Join Date: Jan 2005
Location: USA
Posts: 585
Question

Originally Posted by Speedy Petey

That receptacle will not meet the code required one though.

Can you explain what you mean by this?
 
  #9  
Old 06-13-06, 05:10 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,440
The receptacle in the cabinet will not count as the required GFI receptacle that need to be within 36" of the bowl.
 
  #10  
Old 06-13-06, 05:34 AM
Member
Thread Starter
Join Date: Jan 2005
Location: USA
Posts: 585
But it's OK as a secodary receptacle if we have another wall mounted one within 36" right?
 
  #11  
Old 06-13-06, 12:52 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
Yes.

I am Petey and I approve of this message. Even though they tell me it was too short.
 
  #12  
Old 06-13-06, 12:53 PM
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,623
Originally Posted by syakoban
But it's OK as a secodary receptacle if we have another wall mounted one within 36" right?
Yes, that is fine
 
  #13  
Old 06-13-06, 01:31 PM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Sorry, when I typed 26 inches I did make a mistake. I have corrected it to 36 inches.
 
  #14  
Old 06-13-06, 02:10 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
I guess if I was smart and quoted like JW my post would have been long enough.
 