I am planning on running power to my detached garage. (Right now I am running everything on a 20amp extension cord.) It's about 25 feet from the house. I haven't decided whether to go aerial or underground. The entrance panel is on the wall facing the garage so either way is pretty simple.
I plan on running #8-3 and neutral on a 30amp breaker to a branch panel with 2 circuits for lights (15amp) and two circuits for outlets (20amp). Do I need a separate ground rod for the garage or should I tie into the main panel ground? Or both?
If I go aerial, can I use UF 8-3 with a steel-wire support or do I need some other type of wire?
Thanks,
Hal
I plan on running #8-3 and neutral on a 30amp breaker to a branch panel with 2 circuits for lights (15amp) and two circuits for outlets (20amp). Do I need a separate ground rod for the garage or should I tie into the main panel ground? Or both?
If I go aerial, can I use UF 8-3 with a steel-wire support or do I need some other type of wire?
Thanks,
Hal
#2
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,246
Upvotes: 0
Received 0 Upvotes
on
0 Posts
UF is only suitable for direct burial.
I recommend that you run buried conduit. I suggest more than a 30 amp circuit. I would go at least 60. But if you do run conduit you can always change it later.
You can run a three wire circuit or a four wire circuit. To run a 3 wire circuit there must be no other metal path back to the main building, such as a water pipe, or telephone line, or whatever.
You need a ground rod at the garage.
I recommend that you run buried conduit. I suggest more than a 30 amp circuit. I would go at least 60. But if you do run conduit you can always change it later.
You can run a three wire circuit or a four wire circuit. To run a 3 wire circuit there must be no other metal path back to the main building, such as a water pipe, or telephone line, or whatever.
You need a ground rod at the garage.
#3
Member
To run a 3 wire circuit there must be no other metal path back to the main building, such as a water pipe, or telephone line, or whatever.
I've seen this mentioned several times and I just don't understand it, sorry.
My detached garage has a 3 wire feed but the power comes directly from the meter can, not the main panel like the original poster. Garage has a 100 amp Square D panel with ground rod.
I have cable TV and a phone in the garage, old rotary type. Is this OK?
Thanks,
Baldwin
I've seen this mentioned several times and I just don't understand it, sorry.
My detached garage has a 3 wire feed but the power comes directly from the meter can, not the main panel like the original poster. Garage has a 100 amp Square D panel with ground rod.
I have cable TV and a phone in the garage, old rotary type. Is this OK?
Thanks,
Baldwin