Sub-Panel for Extension
#1
Member
Thread Starter
Join Date: Jul 2006
Location: Logy Bay
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Sub-Panel for Extension
Hi,
I am building an extension on my small 925 sqft bungalow. I have a 125 A panel and was planning on putting a sub-panel in the ext about 35 ft away from the main panel. I have been told that my 125 A service is ok for the additional space, 1500 sq ft in total.
I was wondering about the size of the sub-panel I should use and also the wire type/size I should use for this run? The extension will have only 3 bedrooms, 1 bath and will be electrically heated. The basement will be unfinished but will need some lights/plugs and heat.
Thanks.
I am building an extension on my small 925 sqft bungalow. I have a 125 A panel and was planning on putting a sub-panel in the ext about 35 ft away from the main panel. I have been told that my 125 A service is ok for the additional space, 1500 sq ft in total.
I was wondering about the size of the sub-panel I should use and also the wire type/size I should use for this run? The extension will have only 3 bedrooms, 1 bath and will be electrically heated. The basement will be unfinished but will need some lights/plugs and heat.
Thanks.
#2
Banned. Rule And/Or Policy Violation
Join Date: Feb 2006
Location: North of Boston, MA.
Posts: 1,967
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Why not just upgrade what you have now, and be done with it?
If you just need more ckts, this may be the way to go.
If you just need more ckts, this may be the way to go.
Last edited by mattison; 07-14-06 at 03:16 PM. Reason: No need to quote the entire post above.
#3
Banned. Rule And/Or Policy Violation
Join Date: Feb 2006
Location: North of Boston, MA.
Posts: 1,967
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Why not just upgrade what you have now, and be done with it?
Especialy if going with electric heat.
this may be the way to go.
E
Especialy if going with electric heat.
this may be the way to go.
E
Last edited by mattison; 07-14-06 at 03:17 PM.
#5
Banned. Rule And/Or Policy Violation
Join Date: Feb 2006
Location: North of Boston, MA.
Posts: 1,967
Upvotes: 0
Received 0 Upvotes
on
0 Posts
50 Amp with a 6/3 romex (including ground) should do it.
2-15 amp ckts for bedrooms on AFCI brkrs. 1-20amp ckt for bathroom only. 1-15 amp for the otherlights and recepticals. Then get back with your heat load, Sq' etc.
2-15 amp ckts for bedrooms on AFCI brkrs. 1-20amp ckt for bathroom only. 1-15 amp for the otherlights and recepticals. Then get back with your heat load, Sq' etc.
#6
Experts correct me if I'm wrong but couldn't he install a 200 amp main in the new addition and convert his current 125 amp main to a subpanel? I'm thinking cost wise this might be the middle ground. He must install a panel in the new addition and installing a main wouldn't be that much more unless he was planing a full DIY. Either way wiring must be run to a subpanel so that cost would be about the same.
#7
Banned. Rule And/Or Policy Violation
Join Date: Feb 2006
Location: North of Boston, MA.
Posts: 1,967
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Originally Posted by ray2047
Experts correct me if I'm wrong but couldn't he install a 200 amp main in the new addition and convert his current 125 amp main to a subpanel? I'm thinking cost wise this might be the middle ground. He must install a panel in the new addition and installing a main wouldn't be that much more unless he was planing a full DIY. Either way wiring must be run to a subpanel so that cost would be about the same.
It may not be feasable or economical. Also They would still incure the cost of an upgrade wich they have elected not to do.
#8
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,245
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I think that I would try to stay with a single panel.
My preference would be to replace the main panel with a 200 amp panel. If you cannot afford to upgrade to 200 amp service, then go ahead and use a 125 amp breaker in the new panel, then when you CAN afford it, upgrade the service to 200 amps replace the 125 amp breaker with a 200 amp breaker.
My preference would be to replace the main panel with a 200 amp panel. If you cannot afford to upgrade to 200 amp service, then go ahead and use a 125 amp breaker in the new panel, then when you CAN afford it, upgrade the service to 200 amps replace the 125 amp breaker with a 200 amp breaker.
#9
Member
Thread Starter
Join Date: Jul 2006
Location: Logy Bay
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Originally Posted by racraft
I think that I would try to stay with a single panel.
My preference would be to replace the main panel with a 200 amp panel. If you cannot afford to upgrade to 200 amp service, then go ahead and use a 125 amp breaker in the new panel, then when you CAN afford it, upgrade the service to 200 amps replace the 125 amp breaker with a 200 amp breaker.
My preference would be to replace the main panel with a 200 amp panel. If you cannot afford to upgrade to 200 amp service, then go ahead and use a 125 amp breaker in the new panel, then when you CAN afford it, upgrade the service to 200 amps replace the 125 amp breaker with a 200 amp breaker.
I have an older Commander Q32125 panel. Would I be able to replace the existing breaker in this with a 200 A one? I would probably have to replace the main line to 200 A standard as well but wouldn't have to redo any existing wiring. Is that right or would I have to bring to old part of the house up to code?
Thanks.
#10
No; your old panel is a Q32125 which is a 32 circuit panel rated for 125A. When upgrading a service to 200A, you do not need to bring existing branch wiring up to code.
You do need to replace or improve the following:
* main panel (must be rated for 200A)
* grounding and bonding system (#4 copper to water service + ground rod)
* meter base (usually replace, sometimes provided by power company)
* exterior conduit, riser, mast, weatherhead (1.5" or 2" rigid metal or PVC)
* service conductors (2/0 copper or 4/0 aluminum)
The average price for this upgrade is $1,500 with variation for local labor rates.
You do need to replace or improve the following:
* main panel (must be rated for 200A)
* grounding and bonding system (#4 copper to water service + ground rod)
* meter base (usually replace, sometimes provided by power company)
* exterior conduit, riser, mast, weatherhead (1.5" or 2" rigid metal or PVC)
* service conductors (2/0 copper or 4/0 aluminum)
The average price for this upgrade is $1,500 with variation for local labor rates.
#11
Member
Thread Starter
Join Date: Jul 2006
Location: Logy Bay
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Originally Posted by ibpooks
No; your old panel is a Q32125 which is a 32 circuit panel rated for 125A. When upgrading a service to 200A, you do not need to bring existing branch wiring up to code.
You do need to replace or improve the following:
* main panel (must be rated for 200A)
* grounding and bonding system (#4 copper to water service + ground rod)
* meter base (usually replace, sometimes provided by power company)
* exterior conduit, riser, mast, weatherhead (1.5" or 2" rigid metal or PVC)
* service conductors (2/0 copper or 4/0 aluminum)
The average price for this upgrade is $1,500 with variation for local labor rates.
You do need to replace or improve the following:
* main panel (must be rated for 200A)
* grounding and bonding system (#4 copper to water service + ground rod)
* meter base (usually replace, sometimes provided by power company)
* exterior conduit, riser, mast, weatherhead (1.5" or 2" rigid metal or PVC)
* service conductors (2/0 copper or 4/0 aluminum)
The average price for this upgrade is $1,500 with variation for local labor rates.
I did check my existing svc conductor but I'm not familair with that type a wire, coming from an electronics background. Only the neutral is labeled and it's AWG 2. Is this OK for 200 A or would this need to be replaced?
#12
Banned. Rule And/Or Policy Violation
Join Date: Feb 2006
Location: North of Boston, MA.
Posts: 1,967
Upvotes: 0
Received 0 Upvotes
on
0 Posts
No; your old panel is a Q32125 which is a 32 circuit panel rated for 125A. When upgrading a service to 200A, you do not need to bring existing branch wiring up to code.
Check with the authority on this. Not quite sure where "Logy Bay" is, But here, Panel change ckt change. Enforced.. And thats that. I think they should worry more about tunnles than AFCIs'. But thats just me.
Check with the authority on this. Not quite sure where "Logy Bay" is, But here, Panel change ckt change. Enforced.. And thats that. I think they should worry more about tunnles than AFCIs'. But thats just me.