adding recepticles to an old brick house
Hi All,
I want to do a 20a run for 6-8 recepticles to get our living room rewired. I have only one interior wall recepticle in my plan, the rest need to go along the brick exterior wall. I'll be running the wire in our crawl space. Being that the house is old and I don't want to screw up a whole wall of plaster, what's the easy way to do this? I'm not opposed to the idea of nice flat raceway coming up from the floor (not running along the base of the wall) to a box mounted on the wall but I hate the idea of a junction box under the floor at each outlet so I can join the thhn wire for the raceway to the romex for the run. if it's only 16" of raceway (4 through the floor and 12 above) do I have to use THHN? How might I get these outlets into the wall without making an ugly mess? I'm unwilling to put a recepticle in the floor...what else might I do?
Also, when I wire under the crawl space, can I just tack the wire to the bottom of the floor joists, or does it have to go through?
I want to do a 20a run for 6-8 recepticles to get our living room rewired. I have only one interior wall recepticle in my plan, the rest need to go along the brick exterior wall. I'll be running the wire in our crawl space. Being that the house is old and I don't want to screw up a whole wall of plaster, what's the easy way to do this? I'm not opposed to the idea of nice flat raceway coming up from the floor (not running along the base of the wall) to a box mounted on the wall but I hate the idea of a junction box under the floor at each outlet so I can join the thhn wire for the raceway to the romex for the run. if it's only 16" of raceway (4 through the floor and 12 above) do I have to use THHN? How might I get these outlets into the wall without making an ugly mess? I'm unwilling to put a recepticle in the floor...what else might I do?
Also, when I wire under the crawl space, can I just tack the wire to the bottom of the floor joists, or does it have to go through?
#2
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,245
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Originally Posted by newoldhouse
...but I hate the idea of a junction box under the floor at each outlet so I can join the thhn wire for the raceway to the romex for the run.
Originally Posted by newoldhouse
Also, when I wire under the crawl space, can I just tack the wire to the bottom of the floor joists, or does it have to go through?
#3
Are you saying there are no studs, just plaster on brick? If there are studs I can think of at least three ways to do this without having to repair the plaster afterward and not using surface race. Post back if there is a stud space. I'll post my ways and the experts can correct me if I'm wrong.
#4
Member
Thread Starter
Join Date: Jun 2006
Location: Denver
Posts: 27
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I dind't think my NM could ever be in conduit? to fit it in the flat raceway it would have to come out of the romex and go up the raceway as individual conductors.
Ray, there are no studs. the house is 100 years old. the exterior wall is load-bearing brick, then there's a small void (for insulation) and then another layer of brick inside, more for insulation than structure. The plaster is directly on the brick inside the house.
Ray, there are no studs. the house is 100 years old. the exterior wall is load-bearing brick, then there's a small void (for insulation) and then another layer of brick inside, more for insulation than structure. The plaster is directly on the brick inside the house.
#5
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,245
Upvotes: 0
Received 0 Upvotes
on
0 Posts
NM is allowed to be in conduit when the conduit is for protection. However, it is NOT allowed to strip the outer sheath and use the NM as if it were THHN/THWN.
#6
Member
Thread Starter
Join Date: Jun 2006
Location: Denver
Posts: 27
Upvotes: 0
Received 0 Upvotes
on
0 Posts
ahh...well in that case there's no way I can fit 12-2 into the raceway. that's too bad. Which do you think is more preferable, use the 12-2 romex that I have now and make a junction box in the crawl space for each outlet. Or buy a bunch of single strant THHN that I don't have and conduit that I don't have and just run conduit the whole way around? I could use pvc for ease of use under the crawl space couldn't I? I don't recall seeing anything to join flat raceway to a box, how does one make that connection?
#7
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Originally Posted by newoldhouse
ahh...well in that case there's no way I can fit 12-2 into the raceway. that's too bad. Which do you think is more preferable, use the 12-2 romex that I have now and make a junction box in the crawl space for each outlet. Or buy a bunch of single strant THHN that I don't have and conduit that I don't have and just run conduit the whole way around? I could use pvc for ease of use under the crawl space couldn't I? I don't recall seeing anything to join flat raceway to a box, how does one make that connection?
For the individual conductors you will need to have black, white, green and maybe red (if you plan on any three-wire circuits). If you have more than three current-carrying conductors (the ground wire doesn't count in this particular calculation) then you will need to de-rate all of the conductors. Since this will be in a crawl space you will need to use THWN rated insulation.
As for connecting "flat raceway" to a junction box...they make transition fittings for this purpose. If you plan to drill through the floor and push the "flat raceway" through to the J-box in the crawl space be sure to seal the interior of the raceway with a non-hardening sealer made for electrical purposes.
#8
Member
Join Date: Aug 2005
Location: Indianapolis, IN
Posts: 245
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The big box stores have a whole section of DIY flat raceways, along with connectors, outlet boxes, etc... I have seen wider ones that would fit two 12-2 NM cables, but of course they would be more conspicuous. The packaging will tell you capacities for the conduit.
If this load bearing brick is actually cinder block, you could run armored cable up the channels in the block.
If this load bearing brick is actually cinder block, you could run armored cable up the channels in the block.
#9
Member
Join Date: Jan 2003
Posts: 100
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Originally Posted by racraft
You cannot staple to the bottom of the floor joists. You must either go through the joists or install a running board and staple to the running board.
Check with your inspector. That requirement, for NM cable, applies to Unfinished Basements, not crawlspaces.