Solid or THHN
Old 07-28-06, 08:22 AM
Solid or THHN
On a new service entrance,, anywhere in the code does it state that the ground wire going out to the Ground rods needs to be bare solid or can it be also THHN stranded?
Old 07-28-06, 11:25 AM
Speedy Petey's Avatar
The NEC does not specify. Local codes may.
I use stranded bare.
Old 07-28-06, 11:27 AM
Thanks Petey
Old 07-28-06, 11:40 AM
NEC 250.62 is where you want to look. Grounding electrode conductors may be bare,solid,covered,insulated or stranded. They must be sized to the largest ungrounded service entrance conductor according to Table 250.66. For 200 amp service you need minimum #4 awg copper to any metal water pipe. Maximum #6 awg copper to any ground rod.
Roger
Old 07-28-06, 11:47 AM
Originally Posted by Roger
NEC 250.62 is where you want to look. Grounding electrode conductors may be bare,solid,covered or stranded. They must be sized to the largest ungrounded service entrance conductor according to Table 250.66. For 200 amp service you need minimum #4 awg copper to any metal water pipe. Minimum #6 awg copper to any ground rod.
Roger
I see the #4 for the water line,, but isnt #6 to small since its smaller then the largest current carrying conductor?
hex boy's Avatar
what about 100 amp service could I use #14 awg copper?
Old 07-28-06, 11:52 AM
Read 250.66(A) When connected to rod, plate or pipe (conduit) electrodes......
Old 07-28-06, 12:06 PM
ok,, Just read that section and I now see where your coming from,, Thanks,,,