Two gounding questions
#1
Member
Thread Starter
Join Date: May 2005
Location: Central Florida
Posts: 206
Received 0 Votes
on
0 Posts

1. My workshop sub-panel (60 AMP) is serviced by the main panel with #6-3 plus Ground (#8). I understand that it is recommended that the sub-panel have its own grounding rod installed and connected to the ground bar in the sub-panel. If I do this, do I disconnect the ground wire that goes back to the house, or is leaving it in place OK? Also, is my #8 Ground wire OK to use?
2. I used MC with 12-2 plus ground throughout the workshop. The ground is connected to the GFI receptacles. I’m being told by some that I should also pigtail the ground and connect it to the receptacle boxes. Is this necessary given that I used MC and the receptacles are grounded?
DWC
2. I used MC with 12-2 plus ground throughout the workshop. The ground is connected to the GFI receptacles. I’m being told by some that I should also pigtail the ground and connect it to the receptacle boxes. Is this necessary given that I used MC and the receptacles are grounded?
DWC
#2
Member
Join Date: Jun 2006
Posts: 85
Received 0 Votes
on
0 Posts
ground
1. Without the benefit of the Code Bible to back me up or not, I can not see why you'd need to or should remove the ground back to the house. It seems to me that the feed from the house is protected more surely by its ground wire coming with it.
2. If those switch boxes are metallic, yes--be sure to ground them.
2. If those switch boxes are metallic, yes--be sure to ground them.
#3
Regardless if a separate ground was run with the feeder, YES, you DO need a ground rod for a detached structure with a panel.
If a ground was run you MUST connect it and keep the grounds and neutrals separate in the panel. ONLY the ground bar(s) get bonded to the panel box. The neutral remains isolated.
You should use a #6cu to the ground rod. #8 would need physical protection.
The sheathing on MC is NOT a ground.
You must first and foremost ground metal boxes. With MC this MUST be done with the green grounding conductor.
Grounding devices comes next.
If a ground was run you MUST connect it and keep the grounds and neutrals separate in the panel. ONLY the ground bar(s) get bonded to the panel box. The neutral remains isolated.
You should use a #6cu to the ground rod. #8 would need physical protection.
The sheathing on MC is NOT a ground.
You must first and foremost ground metal boxes. With MC this MUST be done with the green grounding conductor.
Grounding devices comes next.