I've calculated the load that I will have on a circuit, and just wanted to post it here for confirmation.
It is a 15 amp circuit, 14-2 wire feed.

I have, on this circuit:
porch light 1 75W
porch light 2 75W
bedroom fan w/ light 100W
dining room light 100 W

And will be replacing kitchen light with recessed lights, totalling
350W (7 @ 50W each), as well as replacing a kitchen hood exhaust fan (new fan listed as 120V, 60Hz, 1.8 amps, calculated to 216W (I think?)

With 1440W being the max, I come in at 916W

Am I ok on this circuit?

Brian
 
Sponsored Links
  #2  
Old 08-01-06, 09:06 AM
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 2,117
Received 0 Votes on 0 Posts
This is a 15 amp Branch-Circuit with liting outlets and possibly "general-purpose" receptacle outlets. "General-purpose" receptacles are those that supply power to cord-connected loads in bedrooms and living rooms-- loads such as table and floor lamps, radios, phonographs, and very small "intermittent" motor-loads such as a vacuum cleaner.

The "rule of thumb" for such a B-C is 1.5 amps-per-outlet, either a liting outlet or a receptacle outlet, so 10 outlets on a 15 amp B-C would be the extent of the circuit.

Good Luck ,& Learn & Enjoy from the Experience!!!
 
  #3  
Old 08-01-06, 09:14 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Received 0 Votes on 0 Posts
While Pat's rule of thumb is a good rule, it really does not apply here. You have all known loads, so you simply add them up as you have done. You do not have any receptacles.

However, you do not add the loads as you have plan to run them (specific light bulb size), you add the loads based on the maximum per outlet, or location. Based on the fixture ratings, add the maximum size light bulb that can be installed in each location.

If you are still within the maximum for the circuit, then you are okay. If you fall outside this range then you probably should split the circuit.
 
  #4  
Old 08-01-06, 10:06 AM
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,623
Received 0 Votes on 0 Posts
I got 991 watts total which is still within your budgit amps which are correct. This is great as you will surely replace that 100 watt dining room light with a better chandleere in the near future. sorry spelling.
 
  #5  
Old 08-01-06, 10:37 AM
ddr
ddr is offline
Member
Join Date: May 2006
Location: New York City
Posts: 133
Received 0 Votes on 0 Posts
bedroom fan w/ light 100W
I'm assuming the bulb is 100 watts by itself? If so, don't forget to add in the load of the fan, too. If the 100 watts includes everything, sorry about butting in; just wanted to make sure you have the right load.
 
  #6  
Old 08-01-06, 10:46 AM
Member
Thread Starter
Join Date: Jul 2006
Location: Maryland
Posts: 70
Received 0 Votes on 0 Posts
I will have to check on the ceiling fan, but otherwise everything stated was max for each. Thanks for the help!
 
  #7  
Old 08-01-06, 11:26 AM
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 2,117
Received 0 Votes on 0 Posts
Bob, your point is well recieved, but it may help Brian to know he can, if necessary, connect general-purpose receptacle outlets to the circuit he is designing.
 
  #8  
Old 08-01-06, 12:45 PM
Member
Join Date: Jul 2006
Posts: 47
Received 0 Votes on 0 Posts
Why not go ahead and run12/2,, stick it on a 20 Amp breaker,, (just in case) you decide while your running your circuit,, that you might like a outlet somewhere.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: