Wiring a 240v 30a outlet
Just checking....
I just need 10/2 wg correct? I have 10/3 wg. Can I just chop off the neutral or should I hook it up along with the ground?
Thanks,
Dan
I just need 10/2 wg correct? I have 10/3 wg. Can I just chop off the neutral or should I hook it up along with the ground?
Thanks,
Dan
#2
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,530
Upvotes: 0
Received 0 Upvotes
on
0 Posts
What is the outlet for? A dryer for example needs a neutral and a ground. Some other appliance may not.
If you are sure you dont need the neutral, then yes you can just cut it off, or cap it with a wirenut.
If you are sure you dont need the neutral, then yes you can just cut it off, or cap it with a wirenut.
#3
Member
Thread Starter
Join Date: Apr 2006
Location: Arlington
Posts: 172
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Originally Posted by jwhite
What is the outlet for? A dryer for example needs a neutral and a ground. Some other appliance may not.
If you are sure you dont need the neutral, then yes you can just cut it off, or cap it with a wirenut.
If you are sure you dont need the neutral, then yes you can just cut it off, or cap it with a wirenut.

It's actually powering a single 5500w hot water heater element.
#5
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,246
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It does not sound like you need the neutral (straight 240 volt devices do not need them). However, instead of "chopping it off", I recommend capping it (at both ends) and not using it. You don't know when someday you may want to upgrade to a device that needs the neutral and you will curse yourself for cutting it off.