An outside fountain pump runs to a switch/receptical box on an outside wall. In the circuit breaker box is a GFI breaker.

The pump does not work. The receptical works fine. I can not test or rest the GFI breaker at the box.

Does this indicate the breaker is bad?

How big a deal is it to replace a circuit breaker in the main panel?

TIA
 
Sponsored Links
  #2  
Old 08-17-06, 04:22 PM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
If a GFCI breaker will not test then it is either wired wrong or bad.

Replacing a breaker is not difficult, but is probably not a job for an amateur. Getting the RIGHT breaker is sometimes a tricky thing.
 
  #3  
Old 08-17-06, 04:26 PM
Member
Thread Starter
Join Date: Sep 2004
Location: So Cal
Posts: 124
The breaker has been working for about 5 years.

I was just wondering if turning off the main and pulling the panel cover, remove the breaker, install the panel cover, and turn on the main is the correct procedure.
 
  #4  
Old 08-17-06, 04:43 PM
Banned. Rule And/Or Policy Violation
Join Date: Feb 2006
Location: North of Boston, MA.
Posts: 2,113
Fine for 5 years, running a pump? Bad is possable.
If you feel comfortable with the steps you described, Main OFF and then the panel cover off, try this (just remember there are still LIVE EXPOSED parts in this panel)...
Remove the black wire from the breaker... Reinstall the panel cover, Turn on the main. Then reset the GFI inquestion.IE: Off then ON.
If it holds... you have a wire or pump issue.
 
  #5  
Old 09-02-06, 11:56 AM
Member
Thread Starter
Join Date: Sep 2004
Location: So Cal
Posts: 124
I replaced the GFCI breaker today and it tested fine.

My pump would not run so I tested the voltage at the pump and that was good.

I pulled the pump out of the sump and it was shot. The pump over heated and basically melted.

Though the pump is thermally protected, it did seem to matter.

Replace the pump with a spare and things are look good.
 
  #6  
Old 09-02-06, 12:04 PM
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,623
Thanks for posting back Dan. Others may be able to learn from your experience.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes