System ground and system neutral

I resently wired up a 3 prong 220 receptical from a 4 wire source. The welder had no means for equipment ground and was not wired for it. It was a new welder with a 3 wire cord.
The receptical I used for 3 wire system and the wire feeding it was 4 wire bx cable. I attached the ground to the metal box
and the system neutral to the 3rd screw on the receptical
and the 2 hots leads to their respective screws. It all works fine
but I came across something that I dont understand.
First off the circuit is fed by a sub panel with a separate neutral and ground terminal buss . When I started to install the receptical into the gounded metal box a small visual spark on
was noted. I measured the voltage between the ground and the box and read zero but yet the spark was constantly produced when I started to install the receptical. I somehow think its a potential difference between the ground and neutral is creating
the spark but why can't it be read with a meter? It cant be felt with your bare hands either.

Larry
 
Sponsored Links
  #2  
Old 08-31-06, 06:12 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Larry,

You wired things wrong. Your welder needs a ground, not a neutral. A welder is a strsight 240 volt device. As such it needs two hot wires and a GROUND wire, not a neutral wire. Cap the neutral in the receptacle box and do not use it.
 
  #3  
Old 08-31-06, 08:52 AM
Member
Join Date: Aug 2005
Location: USA
Posts: 995
I agree with Racraft. Just to verify, what is this welder's make/model? What are the numbers found on the receptacle and plug?
 
  #4  
Old 08-31-06, 09:14 AM
Member
Thread Starter
Join Date: Oct 2005
Location: USA
Posts: 274
Thanks guys.

Your absolutely right. I bet I have wired hundreds of 3 wire 220 recepticals correctly but this time I guess I went brain dead. It was the first 4 wire supply for a 3 wire device. Thank you so much guys for keeping my wires straight.

Larry
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
'