After reading this forum all morning....I have a couple of questions....
I just bought a new dryer from Sears.....
The outlet I have right now in my wash room is a NEMA 10-50 outlet connected to a 40AMP breaker. (Which doesn't make sense to me either but after reading the forum this morning, this is OK, since this is the only outlet on the wire.)
My question is can I replace this outlet with a NEMA 10-30 outlet?
(I'm thinking the answer is NO! And I will have to have someone come in and rewire everything and install a new breaker and wiring and all that.)
I just bought a new dryer from Sears.....
The outlet I have right now in my wash room is a NEMA 10-50 outlet connected to a 40AMP breaker. (Which doesn't make sense to me either but after reading the forum this morning, this is OK, since this is the only outlet on the wire.)
My question is can I replace this outlet with a NEMA 10-30 outlet?
(I'm thinking the answer is NO! And I will have to have someone come in and rewire everything and install a new breaker and wiring and all that.)
#2
first, since the wire is (or at least should be) properly sized for a 40 amp circuit (due to the 40 amp breaker) the wire is more than large enought to use for a 30 amp circuit.
Code requires the circuit to be no greater than 30 amp if you are using a 30 amp rated recep. Since the wire should be fine (post the size to be sure) other than changing the recep, you would need to replace the 40 amp breaker with a 30 amp breaker.
If you are capable of doing so yourself but need some direction or advice, feel free to ask.
do youreally need the 30 amp recep. I don't do much residential work but it seems most dryer receps are 40 amp.
Code requires the circuit to be no greater than 30 amp if you are using a 30 amp rated recep. Since the wire should be fine (post the size to be sure) other than changing the recep, you would need to replace the 40 amp breaker with a 30 amp breaker.
If you are capable of doing so yourself but need some direction or advice, feel free to ask.
do youreally need the 30 amp recep. I don't do much residential work but it seems most dryer receps are 40 amp.
#3
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,245
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Dryer circuits in the US are 30 amps.
You can only convert this circuit to a 30 amp dryer circuit if the circuit contains FOUR wires. All new circuits for dryers must be four wire. While one could argue that the circuit already exists, and that you are simply changing the breaker and the receptacle, this still implies a new circuit.
You can only convert this circuit to a 30 amp dryer circuit if the circuit contains FOUR wires. All new circuits for dryers must be four wire. While one could argue that the circuit already exists, and that you are simply changing the breaker and the receptacle, this still implies a new circuit.
#4
I'll be darned. I went and looked at mine and it is a 30 amp.
Thanks Bob. Like I said, I claim ignorance on some of the resi stuff. I really muffed this one with the 4 wire as well.
NEMA 14-30R (receptacle) and 14-30P (plug on the whip) are what you need.
I agree with Bob concerning the "new" circuit situation as well. If the current conductor run isn't 4 wire, you do need to change that as well. #10 awg (or larger) is correct sizing for the wire.
Thanks Bob. Like I said, I claim ignorance on some of the resi stuff. I really muffed this one with the 4 wire as well.
NEMA 14-30R (receptacle) and 14-30P (plug on the whip) are what you need.
I agree with Bob concerning the "new" circuit situation as well. If the current conductor run isn't 4 wire, you do need to change that as well. #10 awg (or larger) is correct sizing for the wire.