i know how to add up everything on a planned new circut to see if i am going overload it and need to add another circuit.
but if you are going to add a sub panel, how do you know if your main panel can handle it ?
i can only use 16A on a 20A circuit, correct ?
and i can only use 160A on a 200A panel, correct?
so if i have a 200A main panel using 150A, can i only have a 10A sub panel(10A being whats left of the 160A), or can i have a 200A sub panel?
what is the limit of a sub panel?
or, another way to look at it is, if i have a 200A main panel with a 100A breaker and 5 20A breakers ,with all circuits drawing 80% of max, what amp size sub panel can i add ?
Old 10-04-06, 03:31 AM
Speedy Petey's Avatar
A demand load calculation is the only way to tell if the main service is capable.
BTW- "ALL" circuits will never be at 80% at the same time.
Old 10-04-06, 07:28 AM
You can have a 200A subpanel. The subpanel can be up to the rating of the feeding panel. Technically, you could do a 200A panel to a 200A panel to a 200A panel, etc., so long as the actual load does not exceed the 200A service capability.
A demand load calculation is the way to determine what your service can handle.
http://www.selfhelpandmore.com/homewiringusa/2002/definitions/demandcalc/
Old 10-04-06, 08:04 AM
thanks for the help. and thanks for the link.