Outlet below breaker box, ok to do?

Is it ok to put a 240 outlet(for welder) about 2 feet below my breaker box in the garage, or does this break code? Thanks in advance!
 
Sponsored Links
  #2  
Old 10-14-06, 11:10 AM
Member
Thread Starter
Join Date: Nov 2005
Location: Greeley, Colorado
Posts: 135
OK, I know this is an uninteresting post, but we're gonna do this in a couple of hours, and if anyone know if this is okay to do, the info would be greatly appreciated. Thanks!
 
  #3  
Old 10-14-06, 11:29 AM
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,623
I do not see any problem with this.
 
  #4  
Old 10-14-06, 01:04 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,807
If you can run through the wall NM is ok. If surface mount run EMT (AC would probably be acceptable also).
 
  #5  
Old 10-14-06, 04:33 PM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 5,599
Just don't park the welder in front of the panel. You still need to keep the 30" x36" area clear directly in front of the panel.
 