help with boiler control

Boiler is only 6 months old from last home owner. boiler will not fire when it should i have to push swith in Honeywell box to get boiler to fire.boiler temp was 70 this morning with the circulater pumps running.
 
Sponsored Links
  #2  
Old 11-05-06, 08:43 AM
Banned. Rule And/Or Policy Violation
Join Date: Feb 2006
Location: North of Boston, MA.
Posts: 2,113
Received 0 Votes on 0 Posts
In the controler you should have terminals marked "TT".
with a peice of wire jump these out (just touch them)
and see if the contacts pull in.
Be carefull, the other side of the controler has line (120v)voltage.
If it does pull in, then you may have lost the control transformer,or you have a t-stat issue.

Pix may be helpfull.
 
  #3  
Old 11-05-06, 09:15 AM
Member
Thread Starter
Join Date: Nov 2006
Posts: 7
Received 0 Votes on 0 Posts
is there any way i can test the transformer and the t-stat. The box is a honeywell L8148E Aquastat. Thank You
 
  #4  
Old 11-05-06, 09:33 AM
Member
Join Date: Apr 2004
Location: Ontario Canada
Posts: 1,767
Received 0 Votes on 0 Posts
The control box is considered a sealed unit.

Shorting the thermostat terminals is an acceptible way to test the burner and its control.
 
  #5  
Old 11-05-06, 11:19 AM
Banned. Rule And/Or Policy Violation
Join Date: Feb 2006
Location: North of Boston, MA.
Posts: 2,113
Received 0 Votes on 0 Posts
Question

Aquastat. This could be your combo- High/low limit.
It' possable this is gone, and the low limit is not calling.
Did you try the "TT" yet? If yes and it pulled in... Transformer should be fine.
 
  #6  
Old 11-05-06, 12:29 PM
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 2,117
Received 0 Votes on 0 Posts
. """boiler will not fire when it should----- i have to push swith in Honeywell box to get boiler to fire"""

".boiler temp was 70 this morning with the circulater pumps running."

This description suggest a combustion problem (presuming an oil-fired furnace). The Primary control will open the power-circuit to the burner motor and "lock-off" if the combustion flame is erratic. The Primary control will remain "locked-off" until it is reset.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: