ufer ground wire too large

Reply

  #1  
Old 11-10-06, 04:03 PM
Member
Thread Starter
Join Date: Nov 2006
Posts: 2
ufer ground wire too large

My cement contractor for my new garage supplied the wire for the ground and I find out now it won't fit in the holes in the bus bar.
Is there an acceptable fix for this?
Thanks
 
Sponsored Links
  #2  
Old 11-10-06, 04:10 PM
Banned. Rule And/Or Policy Violation
Join Date: Feb 2006
Location: North of Boston, MA.
Posts: 2,113
Main panel? Perhaps a double lug, tork it correctly.
I may be wrong, but seems like a viable option.
 
  #3  
Old 11-10-06, 04:14 PM
Member
Thread Starter
Join Date: Nov 2006
Posts: 2
Sorry it's a 100 amp sub panel
 
  #4  
Old 11-10-06, 04:20 PM
Banned. Rule And/Or Policy Violation
Join Date: Feb 2006
Location: North of Boston, MA.
Posts: 2,113
To a sub panel. Drill and tap a new lug.
Your ground bus is connected to the can any way.
 
  #5  
Old 11-10-06, 05:54 PM
Member
Join Date: Aug 2004
Location: NA
Posts: 1,065
You most likely can go to the electrical supply and buy an add on oversize lug that will fit the existing ground bar utilizing two of the set screws or other method. All panel makers supply these oversize lugs. At the big box stores L and HD they are on the accessories shelf.

Roger
 
Reply