I am needing to install an in-line duct fan. The fan is 110v, I want to get this fan to cut on when the system's blower comes on. The system's blower is 220v. How can I make this happen? Is it possible?

Thanks in advance,
dogthenine
 
Sponsored Links
  #2  
Old 11-15-06, 03:41 AM
GregH's Avatar
Super Moderator
Join Date: Jan 2001
Location: Manitoba
Posts: 9,672
A device like this would simplify the installation of your fan.

http://www.smarthome.com/3018.html

Check to see if the maker of your fan offers this.
 
  #3  
Old 11-15-06, 08:46 AM
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 2,117
Install a "sail-switch" that will operate when there is air-flow, and will close a contact. The contact-closure can close the 24 volt control-circuit of a switching relay. The switching-relay contacts can switch either a 120 volt load, or a 220 volt load.

See "useful Web Sites" ( beginning of this Forum) for the WSA of the Honeywell "on-line" catalog.
 
  #4  
Old 11-15-06, 05:03 PM
Banned. Rule And/Or Policy Violation
Join Date: Feb 2006
Location: North of Boston, MA.
Posts: 2,113
You will need a seperate source for the 110 fan, and some type of control, such as an end switch/relay to verify flow (sail sw,proof sw, etc.)

Curious, What's the use?
 
  #5  
Old 11-19-06, 10:25 PM
Member
Thread Starter
Join Date: Nov 2006
Posts: 2
I have a room (livingroom/den) that is not getting enough air/heat. My old duct work looked like it had been stepped on and bent back to shape. I replaced it with new duct work and still have the same problem. I think the length of the register from the main source is too far for the main blower to push the air that far. Therefore, I am installing an in-line duct fan.
 
  #6  
Old 11-20-06, 04:23 AM
mattison's Avatar
Member
Join Date: Mar 2003
Location: Cinti, OH
Posts: 5,549
90% of the time these duct fans do not help. If you want to give it a shot a sail switch will get you there.
 
  #7  
Old 11-21-06, 05:02 PM
Banned. Rule And/Or Policy Violation
Join Date: Feb 2006
Location: North of Boston, MA.
Posts: 2,113
You may want to try the HVAC page. For your plans may degrade the entire system.
 