#8 wire

I have some #8 wire left over from installing my air compressor.

Can I use it for a mig welder. The book says I need a 40 amp breaker. Will #8 wire carry 40 amps?

Thank you
 
Sponsored Links
  #2  
Old 11-18-06, 05:19 PM
Member
Join Date: Nov 2006
Location: Twin Falls
Posts: 54
#8 is rated to 40 amps, provided it is COPPER wire.
 
  #3  
Old 11-18-06, 08:08 PM
Banned. Rule And/Or Policy Violation
Join Date: Feb 2006
Location: North of Boston, MA.
Posts: 2,113
Question

Originally Posted by Curious Homeowner
I have some #8 wire left over from installing my air compressor.

Can I use it for a mig welder. The book says I need a 40 amp breaker. Will #8 wire carry 40 amps?

Thank you

This all depends. What and how is this#8 constructed?. Is it a cable? or is it a single conductor?
 
  #4  
Old 11-23-06, 08:20 AM
Member
Thread Starter
Join Date: Dec 2000
Posts: 121
#8 wire

The wire I have is #8 single strand copper.
 
  #5  
Old 11-24-06, 07:52 AM
Banned. Rule And/Or Policy Violation
Join Date: Feb 2006
Location: North of Boston, MA.
Posts: 2,113
I presume stranded (many strands incased in 1 jacket).


Yes you can use this, IF labled THH/WN. It also will need to be installed in some type of conduit with a ground,#10 ins. min.
 
  #6  
Old 11-25-06, 10:15 AM
ElectricalMan's Avatar
Member
Join Date: Feb 2005
Location: Harrisonburg
Posts: 744
Keep in mind 310.3- Stranded Conductors. Where installed in raceways, conductors of size 8 AWG and larger SHALL BE stranded.
 