updating kitchen

Reply

  #1  
Old 11-26-06, 12:52 PM
Member
Thread Starter
Join Date: Sep 2006
Posts: 42
Red face updating kitchen

hi all, was updating kitchen wiring and found all the gfci and regular outlets are rated 15 amp, 120v. but the wiring is 12 gauge 20 amp with 20 amp breakers.(i ass u med they were all the same) do i need to change the gfci and outlets to 20 amp or is this not a bad broblem. thanks
dave
 
Sponsored Links
  #2  
Old 11-26-06, 01:34 PM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
In the US, and I assume you are from the US based on your username, 15 amp receptacles are allowed on 20 amp circuits.
 
  #3  
Old 11-26-06, 01:40 PM
Member
Join Date: Nov 2006
Location: Twin Falls
Posts: 54
Thumbs up

this is not a problem, as stated in NEC 210.21(B)(1), 210.21(B)(2) and 210.21 (B)(3), if a 20 amp circuit serves a single recepticle, that recepticle must be rated 20 amps. If the 20 amp circuit serves more than one recepticle, the recepticles may be rated 15 or 20 amps.
 
  #4  
Old 11-26-06, 01:43 PM
Banned. Rule And/Or Policy Violation
Join Date: Feb 2006
Location: North of Boston, MA.
Posts: 2,113
A "duplex" recept. as you now have, fits this description.
 
  #5  
Old 11-26-06, 01:48 PM
Member
Join Date: Nov 2006
Location: Twin Falls
Posts: 54
and yes, they probably are all the same, you can easily tell without removing them. A 15 amp recepticle looks like this:

|
| |
|

D

in other words, it has a long verticle slot, a short verticle slot, and the D shaped ground.

A 20 amp recepticle looks like this:

|
---| |
|

D

in other words, it has a long verticle slot, a slot shaped like a sideways T and the D shaped ground.
 

Last edited by racraft; 11-26-06 at 03:41 PM.
  #6  
Old 11-26-06, 03:02 PM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
jmchargue,

Your drawing of a 20 amp receptacle is wrong. The long slot is the neutral, and is the slot that is sideways 'T' shaped.
 
  #7  
Old 11-26-06, 03:20 PM
Member
Join Date: Nov 2006
Location: Twin Falls
Posts: 54
ok, yes, that is correct, the other side should be the t shaped slot. my bad.
 
  #8  
Old 11-29-06, 08:04 AM
Member
Thread Starter
Join Date: Sep 2006
Posts: 42
Talking

thank you all !!!!! i never should have started the kitchen to begin with....(never give a hippe a hammer.....lol) but i am glad i did. dave
 