How should I interpret three wire 120/240 or 120/208 volt, 30
AMP? I get the 30 Amp circuit
What does this mean "A four wire connection is preferred"? Does it mean 2 hot, 1 common, 1 grounded? What size wire would I need (12 AWG, 10 AWG?)?
Thanks,
Pete
 
  #2  
Old 12-01-06, 07:03 PM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,245
Upvotes: 0
Received 0 Upvotes on 0 Posts
The range is a dual voltage unit. It needs both 120 volts and 208 or 240 volts.

If this is a new installation in the US you are required to run a four wire circuit. The four wires are two hots, one neutral (also called grounded or return) and one ground.

30 amps only needs 10 gage wire, but if this is a range, I highly recommend at least 8 gage, perhaps even 6 gage wire to allow for future expansion.
 
 