GFI 15Amp Circuit

I need to find out what the NEC Code says about a GFI receptical and what the Mili Amp trip would be for a 15 amp Circuit. I had this question posed to me by someone doing an audit and I do not know what the trip point would be. I know that the manufacturer has to set a trip limit but I do not know what that trip limit is.Thanks
 

Last edited by skippy1955; 12-05-06 at 09:23 AM.
Sponsored Links
  #2  
Old 12-05-06, 10:43 AM
ddr
ddr is offline
Member
Join Date: May 2006
Location: New York City
Posts: 133
Received 0 Votes on 0 Posts
NEC Art. 100-I has an FPN under its definition of a GFCI that states: “Class A ground-fault circuit interrupters trip when the current to ground has a value of in the range of of 4mA to 6mA. For further information, see UL 943, Standard for Ground-Fault Circuit Interrupters.”

As for your specific GFCI, I would contact the manufacturer to see what the listed spec on that model is.
 
  #3  
Old 12-05-06, 12:37 PM
Member
Thread Starter
Join Date: Dec 2006
Posts: 2
Received 0 Votes on 0 Posts
Thanks for your help.
 