220v for a welder

Reply

  #1  
Old 12-09-06, 07:25 PM
Member
Thread Starter
Join Date: Dec 2006
Posts: 3
220v for a welder

i would just like to run this by some experts to insure i am doing this correct.
i have a 40 amp 2 pull braker, 8/3 wire ( because it was free i am using 3 wire) the outlet is rated for 50 amps. now since i will use the black and red for hot and the bare for ground. can i just cap off the white wire at the panel and at the box ? does this sound like a correct install.
 

Last edited by anotherS10; 12-09-06 at 07:55 PM.
Sponsored Links
  #2  
Old 12-09-06, 07:43 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
Yes, just cap off the white and you will be fine.

You say the receptacle is rated for 45 amps? As far as I know there is no such thing.
 
  #3  
Old 12-09-06, 07:55 PM
Member
Thread Starter
Join Date: Dec 2006
Posts: 3
Originally Posted by Speedy Petey View Post
Yes, just cap off the white and you will be fine.

You say the receptacle is rated for 45 amps? As far as I know there is no such thing.
your right its 50 amps. i will change my original post
 