Extending a circuit using smaller wire size

My house uses #12 wire with 20 amp breakers. Can I add a 20 ft lighting extension (2-100w outside flood lamps) from an existing outlet box using #14 wire? Wire will be housed in PVC conduit with pvc box at the end for the light fixture.
 
Sponsored Links
  #2  
Old 12-31-06, 02:17 PM
Member
Join Date: Oct 2005
Location: Milwaukee WI
Posts: 1,338
If you use 14 AWG, you must change the breaker to 15A.

If you use 12 AWG, you can leave the breaker at 20A.

Local codes may vary, but I am not aware of exceptions to this rule.
 
  #3  
Old 12-31-06, 02:39 PM
Banned. Rule And/Or Policy Violation
Join Date: Feb 2006
Location: North of Boston, MA.
Posts: 2,113
Nope. Never heard of local codes overriding NEC. Adding to,Yes.
Run #12 only.
 