How Many Wires?

Using a fish tape and wire lube, and having access tees and els not more than 20 feet apart, can one pull four #10 wires through 1/2-inch conduit?

If not, how about three #10 and three #12 wires in the same conduit? They would of course be on different circuit breakers.
 
Sponsored Links
  #2  
Old 01-03-07, 07:36 AM
T
Member
Join Date: May 2006
Location: McHenry, IL
Posts: 48
Received 0 Votes on 0 Posts
Four #10 wires puts you at 28% fill in EMT, which should be fine.

Three #10 and three #12 puts you at 34% fill, which should still be ok.
 
  #3  
Old 01-03-07, 07:47 AM
A
Member
Join Date: Oct 2005
Location: Milwaukee WI
Posts: 1,339
Received 0 Votes on 0 Posts
Originally Posted by Pipsisiwah View Post
having access tees and els not more than 20 feet apart
Remember that the sum of all bends between pull points (conduit bodies & j-boxes) cannot exceed 360 degrees by code, and the higher your fill ratio, the better off you are to limit that to the lowest number possible.
 