Old 01-07-07, 01:17 PM
What is the largest double pole breaker I can use on 10 gauge bx with a 1/2 circuit length of 38ft? I want to reuse my old hot water heater line for a sub panel to feed my basement, which I am finishing. I found a calculator online but i was confused as to whether to specify 240 or 120 for voltage. Currently it's hooked up to a 30amp dbl pole breaker. Is that already the max?
thks
Old 01-07-07, 01:20 PM
You are doing this backwards. First calculate the load, then the wire and breaker.
no. 10 is limited to 30 amps max regardless of other factors. the load calculator may limit it even further for other reasons.
Old 01-07-07, 06:10 PM
I wanted to know what kind of load I am limited to cause i don't want to run a new wire.
thks
Old 01-07-07, 08:49 PM
R
If the water heater was wired as a typical water heater then you will need to run new wire. A water heater is a straight 240 volt load, and their is no neutral. A 240 volt sub panel needs a neutral.
Old 01-08-07, 05:01 AM
It's a 4 wire circuit. The old heater had 2 elements, one of which was hooked up to a separate meter - I think it only ran at night. So I have 4 wires to work with. Can the neutral be another color other than white if I mark it?
Old 01-08-07, 05:04 AM
R
No. The neutral must be white.