Is 12/3 sufficient to handle a 220 line to support a standard electric dryer, or should I go to 10/3?
 
Sponsored Links
  #2  
Old 01-31-07, 06:14 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
Received 0 Votes on 0 Posts
A dryer is 120/240v, not simply 220v. I do understand though that most non-trade folks do use the term "220v".

99% of "standard" residential electric clothes dryers will require 10/3NM cable on a two-pole 30 amp breaker.

You need the 3-wire because a neutral is required. If this were a straight 240v load you could use 2-wire (10/2 for instance) since no neutral is needed.
 
  #3  
Old 01-31-07, 06:17 PM
Member
Join Date: Nov 2004
Location: CA
Posts: 2,041
Received 0 Votes on 0 Posts
All of the NM cable you will find in your local stores will have a 600 volt rating. And if your circuit was 480 volts at 5 amps you would only require 14 guage. It is the amps that drives wire size. As already stated, a typical dryer is going to require a 30 amp breaker, which would mandate 10 guage wire.
 