Homeline panel board

Reply

  #1  
Old 02-21-07, 07:50 PM
Member
Thread Starter
Join Date: Feb 2007
Posts: 1
Homeline panel board

new 200 amp panel board (42 circuit) does not have sufficient openings for ground and neutral connections. I have approx. 33 circuits in the box. Can I place more than one 12 gauge wire in each hole or must I add an additional ground bar on each side of the panel board. thanks.
 
Sponsored Links
  #2  
Old 02-22-07, 04:36 AM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
You can double and even triple up on like sized grounds.
Neutrals MUST be one to a hole.
 
  #3  
Old 02-22-07, 05:44 AM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
You can also add additional ground bars as needed.
 
  #4  
Old 02-22-07, 07:38 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
A grounding bar kit is only about $5 and available at home centers.
 