I am planning on using electric radiant heat under my 2 new bathrooms. I have 2 systems, each with its own control. They run on 240, the smaller one draws 2.5 amps, and the larger one only 3.0 amps. It seems like I can use one 20 amp 240 gfci breaker to run both....? is this a good idea?
any other suggestions?
 
Sponsored Links
  #2  
Old 03-08-07, 01:59 PM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
Provided your wiring is correct, yes.
 
  #3  
Old 03-08-07, 03:23 PM
Member
Thread Starter
Join Date: Jun 2006
Location: Sugarhouse SLC,Utah
Posts: 123
thanks for your answer...and now more questions....correct wiring!
The instructions call for 2 hot wires into the controller, and the ground from the house connecting directly to the radiant cable. There is no neutral. I assume that I cam use standard 12/2 cable, the black to one connection on the breaker, the white (with a marking tape) to the other, with no neutal leaving the breaker box....
or do I need more help then I thought?
 
  #4  
Old 03-08-07, 03:29 PM
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,973
You are correct. There is no neutral for a straight 240 volt application.
 
  #5  
Old 03-08-07, 03:52 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,533
You may be able to save money on the the GFCI breaker. Many of the electric ceramic tile bathroom floor heaters have GFCI protection built into the thermostat control. A 2 pole GFCI breaker usually runs $60-$150 depending on the manufacturer of your panel. If the thermostats provide GFCI protection, you may use a standard 2-pole breaker.

Also, at that load a 15A breaker with #14 wiring is acceptable instead of the somewhat more expensive #12 wire.
 