Wiring Reversing Switch On 3 Hp Motor

Motor Is Reversing An Has Diagram For Either Cw Or Ccw But I Have A Heavy Duty Reversing Switch It Hase 6 Contacs 3 On Each Side It Came With Wires On Top Left To Bottom Right An Top Right To Bottem Left How Many Wires Do I Need From The Motor To The Switch Note This Is For A Shaper ALSO THE MOTOR IS 110 VOLT 18 AMP THE SWITCH IS 20 AMP ALL SINGLE PHASE
 

Last edited by fibjr; 03-10-07 at 09:37 PM. Reason: AD MORE INFORMATION
  #2  
Old 03-11-07, 07:10 AM
J
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,530
Upvotes: 0
Received 1 Upvote on 1 Post
I do not know what wiring diagram you have. If possible maybe you could post a pic on one of the free sites or link us to one on the mfg web page.

I did look at my Uglys book and all the ones shown there have one wire to the switch for each wire in the motor's cat head.

Edit: I changed the name of the motor's wiring compartment to a more politicly correct one.
 
  #3  
Old 03-11-07, 07:55 AM
nap's Avatar
nap
nap is offline
New Member
Join Date: May 2006
Location: north
Posts: 3,821
Upvotes: 0
Received 2 Upvotes on 2 Posts
Originally Posted by jwhite
I do not know what wiring diagram you have. If possible maybe you could post a pic on one of the free sites or link us to one on the mfg web page.

I did look at my Uglys book and all the ones shown there have one wire to the switch for each wire in the motor's cat head.

Edit: I changed the name of the motor's wiring compartment to a more politicly correct one.
maybe "chicken head" would be better. after all, the prior name is what they do all day long.
or how about "motor lead termination chamber"?

FIBJR: how many leads does the motor have and how are they labled?

and PLEASE do not capitalize the first letter of every word. It makes it difficult for my old eyes to read and I really want to help you through this difficult time. Help me help you.

Just being a bit overly dramatic but it does make it hard to read.
 
  #4  
Old 03-11-07, 08:20 AM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
single phase induction motor 3yl90l-2 120 volt 18 amp 3450 rpm b class date 2006-12 connection z2 ---u2 u1 ---v1 doted line as conected for cw z2----- u1 u2-----v1 are conected for ccw no name on motor but it is a very heavy almost an inch shaft an tefc will help fibjr
 
  #5  
Old 03-11-07, 08:41 AM
J
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,530
Upvotes: 0
Received 1 Upvote on 1 Post
You need four wires plus a ground from the switch to the motor.
 
  #6  
Old 03-11-07, 08:51 AM
nap's Avatar
nap
nap is offline
New Member
Join Date: May 2006
Location: north
Posts: 3,821
Upvotes: 0
Received 2 Upvotes on 2 Posts
thanks for losing tha caps. It helps.

Not sure of your info.

From what I see, you have 4 leads on the motor labeled;

U1, V1, U2, and Z2 and you simply swap the connections as you have listed to reverse the rotation.

and one of the power leads is shown tied to those to each of those connections?

if not please correct me.

post the brand and model of the shaper as well. Maybe we can find some info online to help.
 
  #7  
Old 03-11-07, 08:53 AM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
sounds good j white but now how do i wire it please asb stated befor the switch has 6 contacts top left jumped to bottom right an top right jumped to bottem left do these stay on ?
 
  #8  
Old 03-11-07, 09:05 AM
J
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,530
Upvotes: 0
Received 1 Upvote on 1 Post
You never asked how to wire the switch. You asked how many wires.

do you have a brand name and model number for the switch?

can you ring it out to see what connects to what?
 
  #9  
Old 03-11-07, 09:11 AM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
shaper is a central machinery 1/2 inch wood shaper model # s6851 made in china not i am completly rewireing this shaper because as stated i bought a new heavy switch an the motor was only a 3/4 hp but it was reversible an the very same type of motor but the motor did not work or run now if i hook z2 an u2 together that is one power lead u1 an v1 is the other power lead for cw rotation z2 anz1 is one power lead for ccw an u2 an v1 are the other lead for ccw rotation does this help
 
  #10  
Old 03-11-07, 09:20 AM
J
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,530
Upvotes: 0
Received 1 Upvote on 1 Post
All you need is a heavy duty four way switch, if the motor overloads are internal to the motor.

Does your reversing switch have overloads?
 
  #11  
Old 03-11-07, 09:25 AM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
sorry j white i the heading i ask how to wire reversing switch but the switch is a: h&h2 hp 230vac an note it came with the jumpers i stated befor its a heavy switch probly weighs 2 pounds an has 6 contacts 3 on each side but they are not marked toggle center is pase an off upis on down is on
 
  #12  
Old 03-11-07, 09:31 AM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
motor has a thermal protector on it not it is cap start an cap run also
 
  #13  
Old 03-11-07, 09:37 AM
J
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,530
Upvotes: 0
Received 1 Upvote on 1 Post
Sounds like your switch is double pole double throw center off.

Do you have a tester that you can use to ring out the switch?

I was confused a bit by the use of the term contact. What I guess you meant was connection points.

I will post back shortly with what I believe is the correct wiring.
 
  #14  
Old 03-11-07, 09:39 AM
nap's Avatar
nap
nap is offline
New Member
Join Date: May 2006
Location: north
Posts: 3,821
Upvotes: 0
Received 2 Upvotes on 2 Posts
You run with this one Jeff.

I need info OP is not giving after asking twice and that is only concerning the motor, I didn;t even get to the switch.

I am an electrician, not a dentist.
 
  #15  
Old 03-11-07, 09:48 AM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
j white all info that is on the switch pacage 5930-272-1382 switch toggle dsa 900-69-c-3244 a/7/69 p/naw794 duellman electric co daton ohio this is every thing that is on the switch package
 
  #16  
Old 03-11-07, 10:00 AM
J
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,530
Upvotes: 0
Received 1 Upvote on 1 Post
tks nap I think I understand

fibjr, do you have a tester? I want to check continuity before I give advice. If we get this wrong, the switch will not be the only part you need to replace.
 
  #17  
Old 03-11-07, 10:00 AM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
no i dont know how to ring out the switch an yes the switch has 3 screws on each side to conect the wires to i do not under stand what more info you are asking for sorry i can wire a house but i dont know how to wire this thing it is very confuseing to me
 
  #18  
Old 03-11-07, 10:11 AM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
what kind of tester are you talking about i have a sperry td -2608 tester
 
  #19  
Old 03-11-07, 10:15 AM
R
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,245
Upvotes: 0
Received 0 Upvotes on 0 Posts
fibjr,

Please use proper punctuation and capitalization in your posts. It not only makes you look more intelligent, but it makes them much easier to read. The easier it is to read posts, the more likely you are to get a response

Also, checking your spelling would help. I realize that most of your spelling mistakes are actually typing mistakes, but a spell checker would catch them. They do have spell checkers available for Internet Explorer, Firefox, and most other browsers.
 
  #20  
Old 03-11-07, 10:25 AM
J
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,530
Upvotes: 0
Received 1 Upvote on 1 Post
set your tester for ohms (that is the upside down U symbol. put your leads in comm and ohms

see if the switch has a center off position. meaning it will click into three locations.

remove the jumpers that came pre installed on the switch. put the switch in each position and tell me what shorts to what in each position. be very specific.

also is there a seperate on off switch or is this switch for on off and reverse?
 
  #21  
Old 03-11-07, 10:44 AM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
yes center on the togale is off up is on an down is on
 
  #22  
Old 03-11-07, 10:56 AM
J
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,530
Upvotes: 0
Received 1 Upvote on 1 Post
test the switch and tell me what shorts to what in each position.
 
  #23  
Old 03-11-07, 11:00 AM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
checking every contact on the switch nothing shorts not a one
 
  #24  
Old 03-11-07, 11:08 AM
J
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,530
Upvotes: 0
Received 1 Upvote on 1 Post
first try checking the tester. short the test leads and see if the needle pings.

make sure the tester is set up on ohms, that the batteries are good, and that the leads are in the right holes in the tester.

next view the switch like this from top to bottom.

1..........2
3..........4
5..........6

the switch first in the off positon. nothing should short to anything.

Next try on up.

Next try on down.
 
  #25  
Old 03-11-07, 11:13 AM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
im sorry tog up pos. the 2 bottom screws on each side short in center pos nothing shorts in down pos 2 screws on each side top short
 
  #26  
Old 03-11-07, 11:22 AM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
up is 3 5 an 4 6 short down 1 3 an 4 6 short center nothing shorts
 
  #27  
Old 03-11-07, 11:25 AM
J
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,530
Upvotes: 0
Received 1 Upvote on 1 Post
geez and I provided numbers and everything

I know this is frustrating, but it is the reality of talking in words only over the net. communication can be easily lost. I am trying to be absolutly sure of what you have before I tell you how to wire this. I will not be responsible for your mistakes no matter what, (forum rules) but I still do not want to give out bad advice.

So by the numbers switch up what number shorts to what number and are you sure it shorts to nothing else.

next switch down.. same thing.

I will post a wiring diagram on my web space, and a link to it here as soon as we are positive we have this right.
 
  #28  
Old 03-11-07, 11:27 AM
J
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,530
Upvotes: 0
Received 1 Upvote on 1 Post
check again, down should be 1, 3 and 2, 4
 
  #29  
Old 03-11-07, 11:40 AM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
switch up 3 an 5 short an 4an6 short but not from one side to the other again left side 3an5 right side 4an 6 switch down 1an 3 short an 2an 4 short an again not from the left to the right
 
  #30  
Old 03-11-07, 11:47 AM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
your right my mistake down is 1an 3 and 2an 4
 
  #31  
Old 03-11-07, 11:52 AM
J
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,530
Upvotes: 0
Received 1 Upvote on 1 Post
please verify where the jumpers were originally on the switch.
 
  #32  
Old 03-11-07, 12:26 PM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
going by your #s 1 went from 1---6 an the other went from2---5 in other words from top left to bottom right an from top right to bottom left
 
  #33  
Old 03-11-07, 01:08 PM
J
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,530
Upvotes: 0
Received 1 Upvote on 1 Post
My drawing had a flaw, and I could not find any ready made online.

I am still working on this.
 
  #34  
Old 03-11-07, 01:11 PM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
what happened i said where the jumpers went havent seen nothing since
 
  #35  
Old 03-11-07, 01:19 PM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
no problem j white i have all day just thought we lost contact as you might have guessed im not good on a computer at all an the one im on is as old as the hills but i get by thats about all fibjr
 
  #36  
Old 03-11-07, 02:27 PM
J
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,530
Upvotes: 0
Received 1 Upvote on 1 Post
I have given this my best effort, and I cannot see how this switch can work on this motor.

Did the shaper mfg send you this switch as a replacement part?
 
  #37  
Old 03-11-07, 03:09 PM
nap's Avatar
nap
nap is offline
New Member
Join Date: May 2006
Location: north
Posts: 3,821
Upvotes: 0
Received 2 Upvotes on 2 Posts
OK, let me tag in here. I've had a chance to do some other stuff and willing to give it another shot.

Fibjr, I need you to list all of the leads in the motor.

then list all the connections for CW rotation.

then list all the connections for CCW rotation.


use L1 and L2 as the incoming power leads and include them in your connections.



BTW, realize that we are sitting at our homes doing this because we want to help where we can. We recieve nothing for this other than satisfaction so if you do not recieve an answer as quickly as you think you should, then you would best be served by paying for the advice you are getting here for free. OK?? Just wanted to make that clear.
 
  #38  
Old 03-11-07, 03:14 PM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
to j white no i bought this switch an the motor both off line at ebay but from different sellers
 
  #39  
Old 03-11-07, 03:20 PM
J
Member
Join Date: Apr 2006
Location: New Bern, NC
Posts: 1,530
Upvotes: 0
Received 1 Upvote on 1 Post
Either the switch needs to be 3 pole, the motor needs to be 3 wire instead of four, or we need to incorporate some relay logic into the picture.
 
  #40  
Old 03-11-07, 03:30 PM
F
Member
Thread Starter
Join Date: Mar 2007
Posts: 41
Upvotes: 0
Received 0 Upvotes on 0 Posts
btw i under fully i am in no hurry i just thought at one time i had lost contact as i am not good on a computer now for the motor conections there are 6 total on the motor z2-- u2 --v2

u1-- v1 --z1



z2--u2__________ z2--u1 ___________

u1--v1 ________ line cw u2--v1 ________ line ccw


this is as close as i can draw it note v2-- z1 are not use as they are for caps
 
 