Getting ready for rough inspection

Getting ready for inspector to add some circuits. Close to where the inspector will be looking I have a romex cable running in the garage ceiling toward the top of a 12x4 beam running across the garage. It is attached by staples and was done by previous owners for a refer circuit in the garage. Is it a violation and if it is what is an easy way to protect. I would not have taken this project on if it was not for all the help I get on this site.
 
Sponsored Links
  #2  
Old 03-12-07, 08:49 PM
Member
Join Date: Mar 2005
Posts: 433
Is it a finnished garage? Is it susceptible to damage? If it is unfinished it would be required to be outdoor rated cable or TWHN in conduit .
 
  #3  
Old 03-15-07, 10:39 AM
Member
Join Date: Jun 2006
Location: usa
Posts: 274
Originally Posted by burkej62 View Post
Is it a finnished garage? Is it susceptible to damage? If it is unfinished it would be required to be outdoor rated cable or TWHN in conduit .

Got a code number for that?
Just curious
steve
 
  #4  
Old 03-15-07, 12:17 PM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
In answer to the original question, probably not a code violation.

Hillbilly's implied point is correct. Merely being "unfinished" does not mean that outdoor wiring is required, assuming the garage is dry.
 