Question bonding jumper?

hello, when we wire subpanels for enclosures for machines, i'm having trouble finding in the NEC what size conductor for bonding jumpers for connecting the enclosure doors ,sub panels ,etc. to our main terminal block point. i know when you go by breaker size for say a 60 amp brkr you use 8awg for the equipment bonding jumper, but what about the other things i'm talking about that are just bonding jumpers?
thanks Randy
 
Sponsored Links
  #2  
Old 03-15-07, 05:13 PM
Speedy Petey's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Nov 2003
Posts: 2,455
Received 0 Votes on 0 Posts
I personally am having a hard time understanding your question. You want to bond the doors???

In the NEC we use table 250.122 for this. And for 60 amps the correct EGC is #10cu.

It seems as if you are asking about an industrial setting. This is well out of the scope of DIY work. What is your trade?
 
  #3  
Old 03-15-07, 08:12 PM
Member
Thread Starter
Join Date: Mar 2003
Location: Wisconsin
Posts: 40
Received 0 Votes on 0 Posts
reply

hello, i'm an ind elec/apprentice . in the code book i see where you're talking but does this mean if i want to put a bonding jumper on the doors,we only do this if there's pushbuttons on it, and we put a bonding jumper on the subpanel to the groung terminal blocks, that you use all the same size conductor? it seemed a little confusing in the bonding jumper section in the NEC. thanks
 
  #4  
Old 03-16-07, 10:07 AM
Member
Join Date: Aug 2005
Location: New Jersey
Posts: 247
Received 0 Votes on 0 Posts
See this.

http://www.iaei.org/subscriber/magazine/98_f/simmons_fig2.gif
 
  #5  
Old 03-16-07, 04:01 PM
nap's Avatar
nap
nap is offline
New Member
Join Date: May 2006
Location: north
Posts: 4,163
Received 1 Vote on 1 Post
I cannot find anything that would give you any specifics for size of conductor but here is my take on it.

I would size the bonding jumper to the OCPD of the circuit(s) utilized on the panel door (as a minimum). I would make it no smaller than the largest wire used on the panel door.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: