Quick Wiring Questions
Old 05-07-07, 11:03 AM
Hello all. Just a DIY'er here and just want to pass this thru you experts to make sure I'm ok.
Building a bbq island in backyard. I ran conduit (with 12-3 single copper) which I plan to tap from the outdoor recepatacle in patio to the island.
1) At bbq island, I connected 3 sets of wires to the set from the outdoor receptacle.
a) 1 - 14/3 flex wire for one side of the bbq island (for 2 receptacles)
b) 1 - 14/3 flex wire for the other side, 2 receptacles.
c) 1 - 12/3 stranded running in conduit to back side of bbq island separate from main island. Can I mix the standed and single? Is the 14 gauge flex to 12 gauge feed a problem?
So there are 4 sets of wires I connected in a deep 2 gang juction box. 4 ok?
The receptacles are just for convenience and also to run 1-200w Malibu. The receptacle outside I am feeding of is 15 amp.
Set-up ok?
Thanks.
Old 05-07-07, 11:08 AM
Is this a 15 amp or a 20 amp circuit?
Old 05-07-07, 11:55 AM
the existing receptacle on te patio outside is 15 amp. thanks
Old 05-07-07, 11:58 AM
> I ran conduit (with 12-3 single copper...14/3 flex wire...14/3 flex wire
Specifically what kinds of wire are these? What is printed on the wire or packaging? Is it NM-B cable, UF-B cable, individual THHN/THWN wires, or something else?
> 12/3 stranded
I don't think this exists...
> is the 14 gauge flex to 12 gauge feed a problem?
On a 15A circuit breaker, no. On a 20A circuit breaker, yes.
We need to know the size of the circuit breaker, not the rating of the receptacle.
Old 05-07-07, 12:05 PM
thanks.
1) i bought indiv wires (green, black, white) from home depot. they are 12 gauge, single copper wire inside.
2) 14/3 - sorry, it is just a stranded wires vs. a single copper wire
3) so on a 15 amp, the 12 to 14 connection is ok?
thanks.
Old 05-07-07, 12:11 PM
Is this a 15 amp or a 20 amp circuit. The fact that it is a 15 amp receptacle means does not answer the question. What size is the circuit breaker?
Old 05-07-07, 12:12 PM
It sounds like you are okay as long as the circuit has a 15A _breaker_. You can splice solid and stranded wire with appropriately sized wirenuts that are labeled for use with stranded and solid wire.
Old 05-07-07, 12:21 PM
The circuit is 15 amps
Old 05-07-07, 12:28 PM
Then it is allowed (although not good practice , and considered by some to be poor workmanship) to mix 12 gage and 14 gage wire on the circuit. Be very careful wire nutting together solid and stranded wire.
Hopefully you assembled the conduit first, and then pulled the wires through. Hopefully the wire is THWN. Hopefully you are using outdoor boxes and in use overs for all the receptacles. Hopefully you are connecting to the LOAD side of the GFCI receptacle, or you are using all GFCI receptacles.
Old 05-07-07, 01:39 PM
When shoulld be stranded used? WHen flexibility would be an issue?
Old 05-07-07, 01:53 PM
The trade-off with stranded wire is that it's easier to pull into conduits, but can be more difficult to splice and connect to devices (switches, receptacles).
Old 05-07-07, 02:17 PM
Sorry, one last question. Do I need outdoor boxes if the boxes will be inside the bbq island structure and I am using outdoor receptacle covers? I just bought the remodel blue plastic ones since they will be inside the island but can easily change if necessary (or safer).