connecting a 220 volt airconditioner
Old 06-14-07, 03:48 AM
Smile connecting a 220 volt airconditioner
Hi
I have a 220 volt line in my basement (for a dryer) using 10/3 wire, I don't use this outlet at all but I don't want to take it out.
My question is can I run 10/3 (I'm using 10/3 wire because I have some left over) wire from this outlet to a new 20 amp outlet that I can plug in a 25000 btu airconditioner?
I have a 30 amp breaker in the main panel.
Thanks
Paddy
Old 06-14-07, 05:31 AM
Yes. I recommend taking out the existing receptacle, and just making it a covered junction box for the cables. Just keep it accessible.
You should also replace the breaker with a 20A, because of the ampacity of the new receptacle.
I don't know BTUs. How many amps does it require?
Old 06-14-07, 06:50 AM
amps 13.0/14.1
Thanks for your help, this is the information about the a/c, I don't want to change the breaker if I don't have to.
Power & Ratings:
Amps (Cooling) 13.0 / 14.1 Cord Length 4 ft. Plug Type T blade (tandem) Rated Amps (Receptacle) 20 Volts, Ttl. Connected Load 230 / 208 Watts (Cooling) 2940 / 2880
Old 06-14-07, 07:45 AM
You must change the breaker to 20A for this air conditioner.
Old 06-14-07, 07:47 AM
You need to change the breaker to 20 amps and you need to remove the 30 amp receptacle.
Old 06-14-07, 12:10 PM
Thank you for all your help and advice.