Short to ground
#1
Member
Thread Starter
Join Date: Jun 2007
Location: Detroit
Posts: 3
Received 0 Votes
on
0 Posts

I popped a fuse this morning. I had unplugged the air conditioner and Tv that were plugged in before I attempted to replace the fuse. I was replacing the fuse and as I was screwing it in, the fuse popped again. How would I go about finding the short?
#2
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,970
Received 0 Votes
on
0 Posts
How fo you know it's a short?
Start by unplugging everything and turning off all fixed lights and appliances. If it still pops then you have to start disconnecting portions of the circuit and reconnecting them until you find the problem
Start by unplugging everything and turning off all fixed lights and appliances. If it still pops then you have to start disconnecting portions of the circuit and reconnecting them until you find the problem
#3
Member
Thread Starter
Join Date: Jun 2007
Location: Detroit
Posts: 3
Received 0 Votes
on
0 Posts

I had everything disconnected when I started to install the replacement fuse.... so I assumed. Since posting this I have disconnected each plug and switch from the circuit and disconnected one wire from each receptacle. All of them read open (no reading at all) on the multimeter except one has 15 Ohms. I have started to trace it through the attic but have no clue where it goes.
Am I on the right track??????????
Am I on the right track??????????
#4
Member
Thread Starter
Join Date: Jun 2007
Location: Detroit
Posts: 3
Received 0 Votes
on
0 Posts

Can a fuse box short out? I traced the wire back to a junction box that split the circuit. All of the lines read open except the pair going back to the fuse box. The circuit breaker is removed but I still have continuity.
#6
Member
Join Date: Sep 2003
Location: Central New York State
Posts: 13,970
Received 0 Votes
on
0 Posts
Forget continuity. That test is meaningless unless you are absolutely sure of the wiring.
Add receptacles back one at a time until you either have them all added back and no more blown fuses, or until you find the section where the fuse is blown.
Forget trying to follow the cables in the attic. Just work with receptacles and other boxes on the circuit
Add receptacles back one at a time until you either have them all added back and no more blown fuses, or until you find the section where the fuse is blown.
Forget trying to follow the cables in the attic. Just work with receptacles and other boxes on the circuit