Bedroom Heat on AFCI

I am hardwiring multiple 240V, 1200-1650W electric baseboard heaters in 3 bedrooms. Is it necessary to run these off an AFCI circuit, or can i daisy chain them on dedicated 240V circuit? Or is there a better remedy?
 
Sponsored Links
  #2  
Old 06-26-07, 05:03 AM
Join Date: Mar 2006
Location: Fort Collins, Colorado
Posts: 159
No, since they are 240v they are not required to be AFCI protected.

----------------------------------------------

210.12(B) Dwelling Unit Bedrooms. All 120-volt, single phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit bedrooms shall be protected by a listed arc-fault circuit interrupter, combination type installed to provide protection of the branch circuit.

----------------------------------------------
 