Main Lug

Reply

  #1  
Old 08-02-07, 05:59 PM
Member
Thread Starter
Join Date: Aug 2007
Posts: 1
Cool Main Lug

I have a General Electric cat no. TM1410 model-1 breaker box with a 100 amp main breaker. Can the just the main breaker be change from a 100 amp to a 200 amp breaker, I have six open slots that can be used
 
Sponsored Links
  #2  
Old 08-02-07, 06:26 PM
nap's Avatar
nap
nap is offline
New Member
Join Date: May 2006
Location: north
Posts: 4,163
Doubtful. The panel is rated for 100 amps and that is the largest breaker you can put in as a main. If it would be possible to put in a larger main, you would have to have documentation from GE stating that that specific panel was built with 200 amp rated buss and it is acceptable to install a 200 amp main.

Chances are it would be cheaper and easier in the long run to simply put in a new 200 amp panel.

You would also have to upsize the feeder wires and your service feeders as well as your meter to do this anyway.
 
  #3  
Old 08-02-07, 06:39 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,426
Depending on how you plan on using the 6 open slots you may not need to change the main breaker.

If you have questions about the capacity of your service you should do a load calculation.
 
  #4  
Old 08-02-07, 07:21 PM
HotxxxxxxxOKC's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2006
Location: USA
Posts: 8,044
Sounds like he might be adding up each of his existing breakers and that is at 100 or more, which we all know doesn't matter.
 