splicing wire
I need to flush mount a 50 amp range recp.....I will have to splice the #6 wire together in order to do this...I have access to an area were I can mount a 4in square box to do this....My problem is that the old cable is like a service entrance cable with the nuetral wrapped around the two hot conductors...the two hot conductor are copper and the nuetral I assume is alum...Is this possible?.....My questions are ...1. how do I connect the copper and the alum? ...2. do I need to put some kind of insulation around the alum conductor?....Thanks
#2
Are you saying you need to lengthen the run?
If so this is not allowed by code since you have an SEU cable feeding the range now.
You must re-run the circuit with an 8/3 or 6/3 CU NM cable, or #4AL SER.
If so this is not allowed by code since you have an SEU cable feeding the range now.
You must re-run the circuit with an 8/3 or 6/3 CU NM cable, or #4AL SER.